Protection & Control
Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.
Link copied. Please paste this link to share this article on your social media post.
Hello everybody
Our clients is interested in monitoring temperature and he asks. How many sensors TH110 can support the T300 RTU?. The application is for installing in several SM6-36 inside a MV substation (24.9KV).
Thanks ind advance. @vladimirdo
Link copied. Please paste this link to share this article on your social media post.
Hello,
Do you mean how many TH110/CL110 sensors can be connected to Easergy HU250 embedded ZigBee modem?
I believe up to 60 units.
Regards,
Link copied. Please paste this link to share this article on your social media post.
Yes, limitation is 60 sensors in total
Take care however of the full size of your SM6 equipment(s) if many cubicles in it: zigbee comm will have to cross twice the metallic enclosure, reducing the range to a few meters
Regards
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.