Easergy T300 is a FRTU, a specialized Feeder RTU to control and monitor MV switchgears located in both overhead lines and underground cables MV networks (typically 10 to 36 kV).
Until recently electrical distribution utilities and industrial customers didn't request much from their secondary MV/LV substations: they only wanted them to monitor and report MV faults, measure the load current and operate the MV switchgears. This has changed, customers are now in need of optimizing their MV & LV assets and extending their life while making sure that they are still operational.
For that reason, Schneider Electric has designed specific wireless ZigBee sensors:
Associated to EMS59156 (the optional ZigBee modem for Easergy HU250 module), Easergy T300 FRTU can connect to TH110/CL110 sensors installed in the MV/LV substation:
Easergy T300 being a modular offer, customers have the following choices for condition monitoring:
Link copied. Please paste this link to share this article on your social media post.
Hi All,
In addition to JYP post, you can also see below the link to the White Paper we initiated 2 years ago about Condition Monitoring and which led us to drive the development of the thermal monitoring feature on Easergy T300.
The thermal monitoring feature has been released with firmware version 2.7 together with Easergy HU250 optional ZigBee modem.
Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hi All,
In addition to JYP post, you can also see below the link to the White Paper we initiated 2 years ago about Condition Monitoring and which led us to drive the development of the thermal monitoring feature on Easergy T300.
The thermal monitoring feature has been released with firmware version 2.7 together with Easergy HU250 optional ZigBee modem.
Regards
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.