SmartBuildings - I would like to know why we didn't use redundancy inverter for solar PV plant?
Ask the Community
Ask questions, get advice from experts and peers on Digital Automation & Energy Management.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-02-2110:36 AM
Central inverter are mainly used for large plants with no shading challenges. For a power plant of equal size, we will see the central inverter being the leader on cost and installation time. But it comes with a higher dependency on the supplier.
The design is unique to the manufacturer so if the manufacturer is going to stop his support on that product, the customer could face major cost to get a replacement. With a string inverter, I will have a more flexible solution. The cost will be higher on the CAPEX site but on the other hand I can replace my string inverter much easier by another product.
There are limits to the use of string inverters, if it comes to sophisticated grid support requirements or contractual obligation.
On the service side, central inverter supplier are equipped with strong field service support, string inverter company might not have the setup to fulfil all the service requirements of a large Power Plant.
Long story short, it is less a technical decision as it is much more focused on legal, financial and risk topics.
Jean COMMEIGNES Schneider Electric Community Manager for Power & Building