Briefly Elaborate the difference between the old standards IEC 60439 and new standard IEC 61439?

Highlighted

Briefly Elaborate the difference between the old standards IEC 60439 and new standard IEC 61439?

P;ease guide how the new standard IEC 61439 different from IEC 60439 in terms of safety features of the Panel?

1 REPLY 1
Highlighted
Ensign

Re: Briefly Elaborate the difference between the old standards IEC 60439 and new standard IEC 61439?

Its now more than 10+ years since the launch of IEC61439 series.The following aspects are addressed more effectively in IEC61439 when compared to its predecessor IEC60439:

 

  1. The number of mechanical operating cycles for main contacts and other parts has been increased to 200.
  2. For thermal evaluation - Verification by calculation is limited to a 630A for single compartments & upto 1600A for multiple compartments.
  3. The rated diversity factor is more clearly described, with each circuit requiring a defined rating.
  4. Neutral cross section is raised to a minimum of 50% of phase cross section, valid for PEN conductors too.
  5. Clearance verification by design may be applied utilizing a ‘safety factor’ of 50%.
  6. Shared responsibility between Original Manufacturer vs. ASSEMBLY Manufacturer.
  7. Agreements between Customer and Manufacturer are more detailed and extended.
  8. Concept of Type Testing & Partially Type Testing are replaced by Design Verification.
  9. Routine Tests are replaced by Routine Verification.
  10. Design verification is classified in to 2 categories namely:
    • Constructional Requirement
    • Performance Requirement

 

    11. All constructional requirements are mandatory and to be design verified by testing.

    12. Many new technical terminologies are being introduced namely - Rated Current of an Assembly, Rated Current of a

          Circuit, Group Rated Current of a circuit, Design Current etc

 

The above shared points are few significant differences between IEC60439 & IEC61439. To get familiarized with the design verification methodologies of IEC61439 and its importance, do visit this forum regularly.

   

Regards

S.Saravanan

Principal Technical Expert