Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-04-21 09:05 AM . Last Modified: 2020-11-20 08:56 AM
Question from Georgios Andreadis:
So, we have the right to request verification tests of our specified assembly from the panel builder for every project, before site installation?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-04-21 09:10 AM
Hello,
If the assembly manufacturer used a system from an original manufcaturer and respect the rules from his documentation he would not have to perform additional test.
If there are some deviation(s) based on the comparison between the certification and the assembly to deliver yes additional tests can be performed.
Pascal Lepretre
Sytandardization Officer - Edison Expert
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-04-21 09:10 AM
Hello,
If the assembly manufacturer used a system from an original manufcaturer and respect the rules from his documentation he would not have to perform additional test.
If there are some deviation(s) based on the comparison between the certification and the assembly to deliver yes additional tests can be performed.
Pascal Lepretre
Sytandardization Officer - Edison Expert