Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-08-29 01:44 AM . Last Modified: 2020-11-20 03:53 AM
We have a juice Production line working with a rating voltage of 400 V three phase. it is planned to be moved to another country having a voltage rating of 380 V three phase.
will it work there efficiently? or it needs modifications.
Thanks
Mohammad Obaidat
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-09-02 04:48 AM
Hello,
I don’t see any risk of major malfunction during operation at 380Vac nominal voltage for a system designed for 400Vac. Indeed large majority of equipment designed for 400Vac are applicable to 380Vac. But as we say “The Devil is in the Details.”
To ensure proper functioning of the future installation you should check few things:
Hope it helps.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-09-02 04:48 AM
Hello,
I don’t see any risk of major malfunction during operation at 380Vac nominal voltage for a system designed for 400Vac. Indeed large majority of equipment designed for 400Vac are applicable to 380Vac. But as we say “The Devil is in the Details.”
To ensure proper functioning of the future installation you should check few things:
Hope it helps.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-01 07:14 AM . Last Modified: 2022-02-01 07:16 AM
in line with @MathieuGuillot .
Please take care of the frequenly (50hz or 60 hz) of the network too