Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 10:45 AM . Last Modified: 2022-02-02 01:51 AM
Hello all,
I am writing a paper on the maximization of DER integration and associated overvoltage control. I am looking for some expert opinion on the following matter:
In the time-series analysis scenario; where DERs are integrated, the network nodes might experience overvoltages for short time spans before the voltage comes down below the threshold. My question is, for how long in actual time units, the overvoltage scenario can be allowed in the actual systems. I am looking into the technical reports or papers but they all mention the actual voltage units but not in terms of time for which the overvoltage might be accepted before the tap changers can take action. I would really appreciate any help or a hint towards the direction where I can find some standards to justify my findings.
Thank you very much for taking your time.
Best,
Asif
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-21 05:21 AM
Hello @asif_mtech ,
you can find information in the following standards:
- in figure 44.A2 and Table 44.A2 in Clause 442.2 of IEC 60364-4-44, or
- in figure 12 and Table 5 in Clause 10.2.2.3 of EC 61936-1
Best regards.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-22 11:33 PM
Hello @asif_mtech ,
in complement of @Jacques_P answer, you should also have a look at EN 50160 about Power quality.
In addition, have you check here? 👇
Hope it helps...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-21 05:21 AM
Hello @asif_mtech ,
you can find information in the following standards:
- in figure 44.A2 and Table 44.A2 in Clause 442.2 of IEC 60364-4-44, or
- in figure 12 and Table 5 in Clause 10.2.2.3 of EC 61936-1
Best regards.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-22 11:33 PM
Hello @asif_mtech ,
in complement of @Jacques_P answer, you should also have a look at EN 50160 about Power quality.
In addition, have you check here? 👇
Hope it helps...
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.