Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-05-04 06:37 AM . Last Modified: 2020-11-20 07:59 AM
Hello,
I`m looking for a solution of MCC Panel to be used in IT Network with 525V or 690V.
The combination contactor + breaker needs to achieve 65kA or more.
Could you share your thoughts about that?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-05-05 12:20 AM . Last Modified: 2020-11-20 07:58 AM
Hello,
The ability of a circuit breaker to operate in IT earthing system is covered by the normative Annex H of IEC/EN 60947-2.
All our product TeSys GV and ComPact NSX are compliant to this Annex H for all operating voltages (if not they would be marked with a strikethrough IT). Compact NSX HB1 for instance is suitable for 690V 65kA IT application. (They are used often in 690V Marine application that is 100% IT for instance)
For Contactor there is no special requirement according to earthing system. Circuit-breaker & Contactor coordination tests according to IEC/EN 60947-4-1 are as well not depending of earthing system.
Some additional requirment may exist in some countries. Do you have some special requirments in addition to compliance with IEC/EN 60947-2 and IEC/EN 60947-4-1 in your project ?
Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-05-05 12:20 AM . Last Modified: 2020-11-20 07:58 AM
Hello,
The ability of a circuit breaker to operate in IT earthing system is covered by the normative Annex H of IEC/EN 60947-2.
All our product TeSys GV and ComPact NSX are compliant to this Annex H for all operating voltages (if not they would be marked with a strikethrough IT). Compact NSX HB1 for instance is suitable for 690V 65kA IT application. (They are used often in 690V Marine application that is 100% IT for instance)
For Contactor there is no special requirement according to earthing system. Circuit-breaker & Contactor coordination tests according to IEC/EN 60947-4-1 are as well not depending of earthing system.
Some additional requirment may exist in some countries. Do you have some special requirments in addition to compliance with IEC/EN 60947-2 and IEC/EN 60947-4-1 in your project ?
Regards