Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • Power Distribution IEC
  • :
  • Power Distribution and Digital
  • :
  • Loading limit of number of 10 HP Irrigation Pump Sets on 25 kVA Transformer.Impact of Inrush Current and starting current .
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49427members
Join Now
242732posts
Join Now

Loading limit of number of 10 HP Irrigation Pump Sets on 25 kVA Transformer.Impact of Inrush Current and starting current .

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to Power Distribution and Digital
Solved
ShyamSundarS
ShyamSundarS
Cadet
‎2020-07-07 05:47 AM
0 Likes
4
759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-07 05:47 AM

Loading limit of number of 10 HP Irrigation Pump Sets on 25 kVA Transformer.Impact of Inrush Current and starting current .

In Rural Agricultural Feeders there is a practice of using lower rating transformer for Irrigation Pump set.

In such case observed 25 KVA Transformers are used for loading 10 HP IP sets. The maximum rated current of 25 kVA is 33 A.

There is a possibility of IP set current reaching 18 or 20 A based on the Voltage .

 

So wnated to place this subject for discussion with respect to the motor maximum current for one 10 HP and what would be the condition when two 10 HP are connected to one 25 kVA transformer .Will it reach a overloaded condition.

 

Also what will be the impact of inrush current and motor starting current on the 25 kVA Transformer.

Solved! Go to Solution.

Labels
  • Connectivity
Tags (1)
  • Tags:
  • english
Share
Reply

Accepted Solutions
MathieuGuillot
Lieutenant MathieuGuillot Lieutenant
Lieutenant
‎2020-08-11 07:46 AM
3 Likes
3
689
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-11 07:46 AM

Re: Loading limit of number of 10 HP Irrigation Pump Sets on 25 kVA Transformer.Impact of Inrush Current and starting current .

Hello,

 

Thanks for this very practical question. I am afraid it's not possible to give a general answer. 

 

A 10HP (7,5kW) standard 4P induction motor will have a full load current around 15,5A at 400Vac  

 

A 25kVA transformer can withstand a permanent current of 36A 400Vac. So on the paper a 25kVA transformer can supply two 10HP pump with 15% margin.

 

In practice overload is a question of temperature and duration... so it's difficult to give an answer without considering ambiant T°, duty of motors, possible voltage variations ... 

 

Regarding risk of overolad during motor starting  again it depends of how long last the start, how often it happens, what is the time between two starts ... what is the ambiant temperature...  Transformer can withstand temporary overload, especially liquid immersed. The transformer's manufacturer shall be able to provide such information.

So I can imagine two cases:

- Either the transformer is given and its caracteristics should be known and it's possible to check that it can withstand permanent operation and starting of 2 10HP IP according to ambiant T°, load variations ...   

- Either it's a new installation and the transfomer shall pe specified to operate with 2 10HP pump in a given T° and to withstand the starting charactéristics of the pumps. (Number of start, frequency of starts, starting current, duration ..)  

 

I hope it helps. 

 

Mathieu GUILLOT

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
MathieuGuillot
Lieutenant MathieuGuillot Lieutenant
Lieutenant
‎2020-08-21 06:13 AM
2 Likes
1
643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-21 06:13 AM

Re: Loading limit of number of 10 HP Irrigation Pump Sets on 25 kVA Transformer.Impact of Inrush Current and starting current .

Hello

 

Starting current and duration can be calculated with some software. I am afraid SE is not able to provide you a simple tool to do so but you may find some on the web.

 

To have an accurate calculation you need to know the torque of the pump, at least the type of relationship between the torque and the speed (quadratic, linear ...), its inertia and the characteristics of the electric motor as well. (Starting current, starting torque inertia...)

 

Regards

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
Delcho_Penkov
Crewman Delcho_Penkov Crewman
Crewman
‎2020-08-27 02:09 AM
2 Likes
0
623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-27 02:09 AM

Re: Loading limit of number of 10 HP Irrigation Pump Sets on 25 kVA Transformer.Impact of Inrush Current and starting current .

Hello, such a small motor can have very high inrush current. Therefore the problem of starting will be the voltage drop imposed on the motor already running in parallel. I suppose that the design is standardized, as in the beginning of the message it is said to be a typical practice. Otherwise motor starting may need to be performed with a progressive starter, soft-starter or even to check with VSD, where you can potentially benefit from energy saving.

Best regards,

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
4 Replies 4
MathieuGuillot
Lieutenant MathieuGuillot Lieutenant
Lieutenant
‎2020-08-11 07:46 AM
3 Likes
3
690
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-11 07:46 AM

Re: Loading limit of number of 10 HP Irrigation Pump Sets on 25 kVA Transformer.Impact of Inrush Current and starting current .

Hello,

 

Thanks for this very practical question. I am afraid it's not possible to give a general answer. 

 

A 10HP (7,5kW) standard 4P induction motor will have a full load current around 15,5A at 400Vac  

 

A 25kVA transformer can withstand a permanent current of 36A 400Vac. So on the paper a 25kVA transformer can supply two 10HP pump with 15% margin.

 

In practice overload is a question of temperature and duration... so it's difficult to give an answer without considering ambiant T°, duty of motors, possible voltage variations ... 

 

Regarding risk of overolad during motor starting  again it depends of how long last the start, how often it happens, what is the time between two starts ... what is the ambiant temperature...  Transformer can withstand temporary overload, especially liquid immersed. The transformer's manufacturer shall be able to provide such information.

So I can imagine two cases:

- Either the transformer is given and its caracteristics should be known and it's possible to check that it can withstand permanent operation and starting of 2 10HP IP according to ambiant T°, load variations ...   

- Either it's a new installation and the transfomer shall pe specified to operate with 2 10HP pump in a given T° and to withstand the starting charactéristics of the pumps. (Number of start, frequency of starts, starting current, duration ..)  

 

I hope it helps. 

 

Mathieu GUILLOT

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
ShyamSundarS
ShyamSundarS
Cadet
‎2020-08-13 05:24 AM
0 Likes
2
673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-13 05:24 AM

Re: Loading limit of number of 10 HP Irrigation Pump Sets on 25 kVA Transformer.Impact of Inrush Current and starting current .

Dear Mathieu GUILLOT,

 

Thank you for the appreciation of the practical problem.

 

Yes this issue got evolved during third party inspection of 25 kVA Transformer feeding IP sets .

 

The IP sets will be switched on twice in a day.

 

The transformer rated Voltage is 11/0.433 kV. The Voltage drop in the feeder is in the range of 400 V to 350 V.

 

The ambient in Bangalore Rural is in the range of 20 degree Celisius to 29 Degree Celesius.

 

I wanted to understand what would be the starting current for a 10 HP Motor and its duration, 

 

Thank you Mathieu

 

 

Tags (1)
  • Tags:
  • english
Share
Reply
MathieuGuillot
Lieutenant MathieuGuillot Lieutenant
Lieutenant
‎2020-08-21 06:13 AM
2 Likes
1
644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-21 06:13 AM

Re: Loading limit of number of 10 HP Irrigation Pump Sets on 25 kVA Transformer.Impact of Inrush Current and starting current .

Hello

 

Starting current and duration can be calculated with some software. I am afraid SE is not able to provide you a simple tool to do so but you may find some on the web.

 

To have an accurate calculation you need to know the torque of the pump, at least the type of relationship between the torque and the speed (quadratic, linear ...), its inertia and the characteristics of the electric motor as well. (Starting current, starting torque inertia...)

 

Regards

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
Delcho_Penkov
Crewman Delcho_Penkov Crewman
Crewman
‎2020-08-27 02:09 AM
2 Likes
0
624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-27 02:09 AM

Re: Loading limit of number of 10 HP Irrigation Pump Sets on 25 kVA Transformer.Impact of Inrush Current and starting current .

Hello, such a small motor can have very high inrush current. Therefore the problem of starting will be the voltage drop imposed on the motor already running in parallel. I suppose that the design is standardized, as in the beginning of the message it is said to be a typical practice. Otherwise motor starting may need to be performed with a progressive starter, soft-starter or even to check with VSD, where you can potentially benefit from energy saving.

Best regards,

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
Top Experts
User Count
Panel_Rhone_Alp
Lieutenant Panel_Rhone_Alp
2
Arunprasad
Lieutenant Arunprasad Lieutenant
1
SebTTG
Ensign SebTTG Ensign
1
MaïlysseG
Ensign MaïlysseG Ensign
1
Fabien_Mastrot
Lieutenant JG Fabien_Mastrot Lieutenant JG
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric