Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-04-21 09:22 AM . Last Modified: 2020-11-20 08:56 AM
Question from Conrad:
Is the rated diversity factor applicable for sizing the main horizontal busbar?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-04-21 09:32 AM
Hello,
Based on markets (buildings or critical sites), Most of customers prefer to keep the cross section for the full current or to have the same or above current busbar compare to the main incoming section.
The diversity factor is mainly used to distribution busbar
Because we know the loads and so the rating of the different outgoing running at the same time.
In that case we case define and use a diversity factor.
Pascal Lepretre
Standardization Officer - Edison Expert
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-04-21 09:32 AM
Hello,
Based on markets (buildings or critical sites), Most of customers prefer to keep the cross section for the full current or to have the same or above current busbar compare to the main incoming section.
The diversity factor is mainly used to distribution busbar
Because we know the loads and so the rating of the different outgoing running at the same time.
In that case we case define and use a diversity factor.
Pascal Lepretre
Standardization Officer - Edison Expert