Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-04-21 09:12 AM . Last Modified: 2020-11-20 08:56 AM
Question from Alvin,
Is it logical or allowed to install thermal monitoring into the busbar compartment? does it affect the type test?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-04-21 09:16 AM
Hello,
If the system is designed by an original manufacturer, and certified IEC 61439, the system I supposed need to be installed based on a specific documentation. This documentation has been established to guarantee and keep the IEC 61439 performance. In case of doubt additional document as "conformity declaration" can be provide to asset this additional topic.
Pascal Lepretre
Standardization Officer - Edison Expert.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-04-26 03:11 AM
The installation of the thermal monitoring sensor in the busbar compartment must be tested for insulation.
In MV cubicles, for example, certain ranges of switchgear are prohibited for adding sensors to the busbar compartment because this no longer ensures insulation resistance.
For the LV, it is recommended to return to the manufacturer so that it confirms the feasibility.
Stay Safe,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-04-21 09:16 AM
Hello,
If the system is designed by an original manufacturer, and certified IEC 61439, the system I supposed need to be installed based on a specific documentation. This documentation has been established to guarantee and keep the IEC 61439 performance. In case of doubt additional document as "conformity declaration" can be provide to asset this additional topic.
Pascal Lepretre
Standardization Officer - Edison Expert.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-04-26 03:11 AM
The installation of the thermal monitoring sensor in the busbar compartment must be tested for insulation.
In MV cubicles, for example, certain ranges of switchgear are prohibited for adding sensors to the busbar compartment because this no longer ensures insulation resistance.
For the LV, it is recommended to return to the manufacturer so that it confirms the feasibility.
Stay Safe,