Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-04-21 07:57 AM . Last Modified: 2020-11-20 08:56 AM
Question from Daniel Deveze
In the Webinar presentation, there is an information to the change to the maximum rating current to an assembly, to perform an insulation resistance to routine test. Can you explain more?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-04-21 08:03 AM
Hello,
As introduce during this webinar, the IEC 61439 edition 3 shall be published before mid of 2020. In the actual edition 2 for the routine test regarding dielectric performance the assembly manufacturer is authorized to perform an insulating resistance to assembly up to the rating 250A. For upper rating he has to perform a dielectric test. In the next edition 3 the rating is moved up to 630A. For upper rating he has to perform a dielectric test.
Pascal Lepretre
Standardization officer - Edison Expert.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-04-21 08:03 AM
Hello,
As introduce during this webinar, the IEC 61439 edition 3 shall be published before mid of 2020. In the actual edition 2 for the routine test regarding dielectric performance the assembly manufacturer is authorized to perform an insulating resistance to assembly up to the rating 250A. For upper rating he has to perform a dielectric test. In the next edition 3 the rating is moved up to 630A. For upper rating he has to perform a dielectric test.
Pascal Lepretre
Standardization officer - Edison Expert.