Question from Islam Amer
"in some projects, assembler send a sample for type test , can this consider as type tested panel?"
Solved! Go to Solution.
Hello,
My answer can be YES if the sample is verified to be at the end ONE verified assembly
My answer can, be NO if the sample is to cover a full catalogue or several rating of a range of assembly.
For the most difficult tests as temperature-rise and short-circuit,
To cover a full range of rating of an offer, my usual answer is to say there is a need to present several configurations. It is difficult to imagine to present one assembly at 3200A and imagine it will cover the range between 630 - 3200.
Depending the certification body requirements perhaps the needs would be 3 configurations or 4 depending the design changes between the different rating. You have to know more and more business require to have one certification to one rating.
To the short-circuit, to cover a full range of catalogue, it is useful to demonstrate your tests are based on the worst cases and cover the other part of your catalogue.
Best regards,
Pascal Lepretre
Standardization officer - Edison Expert.
Hello,
My answer can be YES if the sample is verified to be at the end ONE verified assembly
My answer can, be NO if the sample is to cover a full catalogue or several rating of a range of assembly.
For the most difficult tests as temperature-rise and short-circuit,
To cover a full range of rating of an offer, my usual answer is to say there is a need to present several configurations. It is difficult to imagine to present one assembly at 3200A and imagine it will cover the range between 630 - 3200.
Depending the certification body requirements perhaps the needs would be 3 configurations or 4 depending the design changes between the different rating. You have to know more and more business require to have one certification to one rating.
To the short-circuit, to cover a full range of catalogue, it is useful to demonstrate your tests are based on the worst cases and cover the other part of your catalogue.
Best regards,
Pascal Lepretre