Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-07-25 05:21 AM
Hi,
I have an issue trying to create projects within EcoSturxure Power Commission using the PAS600L Panel Server units.
I can add devices connected to a Panel Server such as power meters to a project from which I generate reports, just I I have done with other gateway devices, such as the EGX150s which is fine, but for some reason, when I connect to IFMs and subsequently to NSX breakers with BSCM modules, although the devices show up as Modbus connected devices, when I try to add these to a project, I get a splash screen stating "Unable to add devices" as per the attached image. I note that there is no Device Type noted on the device listing either.
Is there anyone that can shed light as to how to add these IFMs/MCCBs to a project as shown?
Thanks in anticipation,
Brian
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-07-25 06:36 AM . Last Modified: 2023-07-25 06:45 AM
Hello @BrianW ,
What is your EPC version and Panel Server FW ?
With EPC 2.28 + PAS800 v001.006.000 this is working.
NSX connected to IFE + IFM are discovered by EPC:
And added to the PAS800:
Devices are then available on the PAS800 Web Pages:
Regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-07-25 06:36 AM . Last Modified: 2023-07-25 06:45 AM
Hello @BrianW ,
What is your EPC version and Panel Server FW ?
With EPC 2.28 + PAS800 v001.006.000 this is working.
NSX connected to IFE + IFM are discovered by EPC:
And added to the PAS800:
Devices are then available on the PAS800 Web Pages:
Regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-07-25 08:39 AM
Hi Romain,
I am not sure if there is a huge difference between the PAS800 and the PAS600L that I am using here, but either way, a quick upgrade to the latest version of EPC and upgrading the PAS600L to the newest firmware certain worked and I am now able to both view and use the serial devices in a project.
Many thanks for your speedy response and correct information!
Best regards,
Brian