Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-10-11 03:02 PM
Can Asset Advisor monitor Power? Voltage, Amperage, etc.
Can Asset Advisor gather the information from a power monitor?
Being able to gather the temperature as well as the power information would provide more insight into the health of an asset.
I have seen some information that Asset Advisor can monitor a MV VFD. How does it accomplish the power monitoring? What does the architecture look like?
Regards,
Saul
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-10-13 08:46 AM . Last Modified: 2023-10-13 08:49 AM
Hi Saul,
Can Asset Advisor monitor Power? Voltage, Amperage, etc.
Can Asset Advisor gather the information from a power monitor?
Device (modbus most of the time) ==> gateway ==> Asset Advisor
Being able to gather the temperature as well as the power information would provide more insight into the health of an asset.
I have seen some information that Asset Advisor can monitor a MV VFD. How does it accomplish the power monitoring? What does the architecture look like?
Perhaps, this link can help you:
https://www.se.com/ww/en/download/document/998-20671877_EAA_Drives/?ssr=true
Best regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-10-16 03:03 AM
Hi Saul,
Connectivity for ATV6000 is made by Com'X, which is installed and configured at factory, not in brownfield once equipment is shipped to customer site. They keep using Com'X by the time all models are created, tested and validated for Panel server. Any ATV6000 ordered with EAA option gets 1 Com'X inside, with all relevant signals. Picture you shared is definition for connectivity with full scope of options.
Regards... Victor Marina
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-10-17 01:58 AM
Hi Saul,
In addition to Loic comment, ATV6000 Drive has their own means to measure current, voltage, energy and power. Following table shows measurements ATV6000 Drive can push into gateway (Com'X or PaS), in turn, into Asset Advisor application (label with Capital letter code correspond with ATV internal coding, same available in ATV6000 manual):
Drive rate - NCV |
Drive rate voltage- VCAL |
Electrical energy Input GWh – IE3 |
Electrical energy Input kWh – IE1 |
Electrical energy Input MWh – IE2 |
Electrical energy Input TWh – IE4 |
Electrical energy Input Wh – IE0 |
Electrical energy Output GWh – OE3 |
Electrical energy Output kWh – OE1 |
Electrical energy Output MWh – OE2 |
Electrical energy Output TWh – OE4 |
Electrical energy Output Wh – OE0 |
Main estimated current phase 1 |
Main estimated current phase 2 |
Main estimated current phase 3 |
Main frequency - FAC |
Main unbalance voltage - UMV |
Main voltage - ULN |
Main voltage phase 1 |
Main voltage phase 2 |
Main voltage phase 3 |
Mains active power P – IPRW |
Mains apparent power S - ISRW |
Mains reactive power Q - IQRW |
Power factor Cos - PWF |
Power input mains current – PIMC |
Power input mains voltage – PIMV |
Power input transformer power - PITP |
Power output Cell Current - PoCC |
Power output cell number - PoCN |
Power output Cell type - PoCT |
Power output cell voltage – PoCV |
I hope this clarifies your question about how Power/energy information
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-10-13 08:46 AM . Last Modified: 2023-10-13 08:49 AM
Hi Saul,
Can Asset Advisor monitor Power? Voltage, Amperage, etc.
Can Asset Advisor gather the information from a power monitor?
Device (modbus most of the time) ==> gateway ==> Asset Advisor
Being able to gather the temperature as well as the power information would provide more insight into the health of an asset.
I have seen some information that Asset Advisor can monitor a MV VFD. How does it accomplish the power monitoring? What does the architecture look like?
Perhaps, this link can help you:
https://www.se.com/ww/en/download/document/998-20671877_EAA_Drives/?ssr=true
Best regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-10-13 12:45 PM
Thank you Loic. Attached you will find the slide of the ATV6000.
It would be interesting to find out what the architecture looks like.
ATV6000 Modbus TCP--->Panel Server--->EAA?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-10-16 03:03 AM
Hi Saul,
Connectivity for ATV6000 is made by Com'X, which is installed and configured at factory, not in brownfield once equipment is shipped to customer site. They keep using Com'X by the time all models are created, tested and validated for Panel server. Any ATV6000 ordered with EAA option gets 1 Com'X inside, with all relevant signals. Picture you shared is definition for connectivity with full scope of options.
Regards... Victor Marina
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-10-16 07:40 AM
Victor,
Thank you for your reply.
Is it safe to assume that the ATV6000 communicates to Com'X via Modbus to get the input power and output power information?
Regards,
Saul
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-10-17 01:14 AM
Hi,
After a check, I confirm the ATV6000 is supported by PanelServer (PAS600 & PAS800).
There is a custom model, that allow PanelServer to monitor all useful data.
The architecture you first asked is possible yet:
ATV6000 Modbus TCP--->Panel Server--->EAA
About the PM8244, yes there is also a custom model for Panel Server allowing :
PM8000 --->Panel Server--->EAA
Important : the custom models I talk here are designed for EAA use, so not all the modbus map are monitored, only the data that EAA need.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-10-17 01:58 AM
Hi Saul,
In addition to Loic comment, ATV6000 Drive has their own means to measure current, voltage, energy and power. Following table shows measurements ATV6000 Drive can push into gateway (Com'X or PaS), in turn, into Asset Advisor application (label with Capital letter code correspond with ATV internal coding, same available in ATV6000 manual):
Drive rate - NCV |
Drive rate voltage- VCAL |
Electrical energy Input GWh – IE3 |
Electrical energy Input kWh – IE1 |
Electrical energy Input MWh – IE2 |
Electrical energy Input TWh – IE4 |
Electrical energy Input Wh – IE0 |
Electrical energy Output GWh – OE3 |
Electrical energy Output kWh – OE1 |
Electrical energy Output MWh – OE2 |
Electrical energy Output TWh – OE4 |
Electrical energy Output Wh – OE0 |
Main estimated current phase 1 |
Main estimated current phase 2 |
Main estimated current phase 3 |
Main frequency - FAC |
Main unbalance voltage - UMV |
Main voltage - ULN |
Main voltage phase 1 |
Main voltage phase 2 |
Main voltage phase 3 |
Mains active power P – IPRW |
Mains apparent power S - ISRW |
Mains reactive power Q - IQRW |
Power factor Cos - PWF |
Power input mains current – PIMC |
Power input mains voltage – PIMV |
Power input transformer power - PITP |
Power output Cell Current - PoCC |
Power output cell number - PoCN |
Power output Cell type - PoCT |
Power output cell voltage – PoCV |
I hope this clarifies your question about how Power/energy information
Link copied. Please paste this link to share this article on your social media post.