Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • Power Distribution IEC
  • :
  • Power Distribution and Digital
  • :
  • Arc Fault Detection
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49400members
Join Now
242680posts
Join Now

Arc Fault Detection

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to Power Distribution and Digital
Solved
SA-Energy
Crewman SA-Energy
Crewman
‎2019-04-02 08:01 AM
2 Likes
1
1366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-04-02 08:01 AM

Arc Fault Detection

I have seen in different North American sites multiple references to Arc Fault Detection solutions.
I struggle to find such solutions in IEC markets.

Is there any reason for that? Would such solutions exist in Europe?

Thanks

Solved! Go to Solution.

Tags (3)
  • Tags:
  • Arc Fault Detection
  • Fire prevention
  • Workforce security
Share
Reply

Accepted Solutions
Zakaria_BELHAJA
Crewman Zakaria_BELHAJA Crewman
Crewman
‎2019-04-02 08:40 AM
5 Likes
0
1359
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-04-02 08:40 AM

Re: Arc Fault Detection

Thank you for this question.

The Arc Fault Detection Devices (AFDD) exist in the European market since 2014.

The product standard that describes the performances of this type of protective devices, IEC 62606, has been released in 2013, and since 2014, the IEC 60364 (installation standard) recommends the use of AFDD in residential and buildings installations:

  • in Sleeping accommodations: e.g. bedrooms (in residential), hotels, nursing home
  • in Locations with risks of fire due to the nature of processed or stored materials: e.g. barns, woodworking shops, stores of combustible materials
  • in Locations with combustible constructional materials: e.g. wooden buildings
  • in Fire propagating structures: e.g. high rise buildings
  • in Locations with endangering of irreplaceable goods: e.g. museums

For more information, please consult:

  • The AFDD dedicated webpage: https://www.schneider-electric.com/en/home/renovation/home-protection.jsp 
  • a whitepaper: https://www.schneider-electric.com/en/download/document/EDCED117020EN/

 

Best Regards;

AFDD offer manager

See Answer In Context

Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
1 Reply 1
Zakaria_BELHAJA
Crewman Zakaria_BELHAJA Crewman
Crewman
‎2019-04-02 08:40 AM
5 Likes
0
1360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-04-02 08:40 AM

Re: Arc Fault Detection

Thank you for this question.

The Arc Fault Detection Devices (AFDD) exist in the European market since 2014.

The product standard that describes the performances of this type of protective devices, IEC 62606, has been released in 2013, and since 2014, the IEC 60364 (installation standard) recommends the use of AFDD in residential and buildings installations:

  • in Sleeping accommodations: e.g. bedrooms (in residential), hotels, nursing home
  • in Locations with risks of fire due to the nature of processed or stored materials: e.g. barns, woodworking shops, stores of combustible materials
  • in Locations with combustible constructional materials: e.g. wooden buildings
  • in Fire propagating structures: e.g. high rise buildings
  • in Locations with endangering of irreplaceable goods: e.g. museums

For more information, please consult:

  • The AFDD dedicated webpage: https://www.schneider-electric.com/en/home/renovation/home-protection.jsp 
  • a whitepaper: https://www.schneider-electric.com/en/download/document/EDCED117020EN/

 

Best Regards;

AFDD offer manager

See Answer In Context

Share
Reply
Top Experts
User Count
Panel_Rhone_Alp
Lieutenant Panel_Rhone_Alp
2
Arunprasad
Lieutenant Arunprasad Lieutenant
1
SebTTG
Ensign SebTTG Ensign
1
MaïlysseG
Ensign MaïlysseG Ensign
1
Fabien_Mastrot
Lieutenant JG Fabien_Mastrot Lieutenant JG
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric