Posted: 2021-11-21 04:35 AM
salam
bgmana cara membuat komunikasi antara plc bmx p34 2020 via tcp/ip egx300 / linx150 ke modbus rtu plc bmx p34 1000
Posted: 2021-11-23 05:07 AM
dari sisi M340 (2020) jika tidak menggunakan NOE, harus menggunakan Readvar (block program) untuk komunikasi ke luar.
kemudian karena di sisi M340 (1000) tidak ada port Ethernet, jadi port serial harus di setting sebagai Slave. selebihnya tidak perlu setting lain-lain lagi disisi M340 (1000). kemudian di sisi gateway (EGX) hanya perlu di setting IP.
kemudian lebih banyaknya adalah setting Readvar di M340 (2020) nya, untuk setting IP target EGX + Id slave, serta register-register yang akan dibaca.
Posted: 2021-11-23 05:38 PM
halo pak rifki
terima kasih sebelumnya
sisi 2020 sdh ada noe. dan sdh sukses scan modbus adress device non plc. ( pm dan altivar )
yg belum saya scan adalah plc devce ( 1000 )
sdh saya config untuk scan di noe.
di 1000 serial port sdh slave. tapi tidsk mendapat response dr 1000..apakah di 1000 di perlukan routine program tertentu? atsu membutuhkan konfigurasi lain diluar variabel u program ( ladder yg telah bsrjalan ) ?