Posted: 2019-12-13 04:47 PM
Ada yang tau ini kenapa? Dan gimana cara mengatasinya?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-12-13 04:54 PM
Ini biasanya gara-gara ada ngerubah property terkait setting trend server atau trend tags nya. Atau ganti nama project.
Resolution:
Hapus semua trend data. Lokasinya menyesuaikan setting lokasi di trend tags masing-masing. Default nya ada di Folder "data" citect
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-12-13 04:54 PM
Ini biasanya gara-gara ada ngerubah property terkait setting trend server atau trend tags nya. Atau ganti nama project.
Resolution:
Hapus semua trend data. Lokasinya menyesuaikan setting lokasi di trend tags masing-masing. Default nya ada di Folder "data" citect
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-06-11 10:34 PM
Anyone Help me on my case citect scada 2018.
I want to input int data type on supergenies then give data to metadata genies and builder.
My project is to get data from button command to give 1-9 bit to enable open valve by supergenies.
I was try give instruction
On SG : ?int AVselect?
On genies : %AVselect%
Builder Variable : AV select to PLC1_avselect(tag variable int type)
But it still not works.
Need your support advice please. Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-10-19 01:46 AM
Saya juga mengalami hal yang sama. Saya telah menghapus data history trend dalam folder "data".
Tetapi belum solve.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-14 11:30 PM
Saya sudah lakukan hal tersebut,
sudah re-start trend server, Compile ulang, re-compile setup wizard, Restart All server,
dan masih tidak bisa nih Pak Rifqi,
Ada solusi lain pak?