One of the easiest ways to reduce Incident energy of down stream Distribution on a Service Entrance Swbd, is to separate the Main Disconnect from the rest of the lineup.
If the Main has bottom incoming and top outgoing lugs, you can provide a Top Hat above the Main Section. On the Distribution Section, you can provide incoming top Lugs with a Top Hat above the incoming Lug Section, then conduit across to connect the two lineups. I would use some type of fire barrier sealant to make sure the arch can not propagate between the two sections.
Even if you separate the two lineups by a foot, the Distribution is no longer dangerous, and if you employ a Maintenance Switch on the Main, you could reduce the Incident energy considerably.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-12-23 01:37 PM . Last Modified: 2020-12-23 01:47 PM
Thanks for the helpful information @JLStanton !
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-12-23 01:37 PM . Last Modified: 2020-12-23 01:47 PM
Thanks for the helpful information @JLStanton !
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.