basic guess: 48" by 36" by 90" tall.
Originally posted by johnwhitcraft on 12/16/2018
Solved! Go to Solution.
If you need an 800A wall mount panelboard, we have several different I-line distribution panels to offer, each with different sizes depending on the quantity and ampacity of branch breakers your are needing. The interior types available are HCM, HCP-SU, HCP, and HCR-U.
I have attached the digest pages that show the size of each along with their limitations. If you are looking for a worst case scenario panelboard size, you could use the dimensions of the HCR-U which are 44"W x 9.5"D x 86"T. The HCR-U has a total of 108" of mounting space.
Originally posted by Brian Ohlendorf - 9 months ago
If you need an 800A wall mount panelboard, we have several different I-line distribution panels to offer, each with different sizes depending on the quantity and ampacity of branch breakers your are needing. The interior types available are HCM, HCP-SU, HCP, and HCR-U.
I have attached the digest pages that show the size of each along with their limitations. If you are looking for a worst case scenario panelboard size, you could use the dimensions of the HCR-U which are 44"W x 9.5"D x 86"T. The HCR-U has a total of 108" of mounting space.
Originally posted by Brian Ohlendorf - 9 months ago
John, as we have discussed by phone & e-mail, the PG&E utility aspects of your request introduced more discussion & documents of the Square D Speed-D versus standard QED2 solution.
They key is the 400A fixed mounted breakers with meter sockets. You have the drawings of the most viable standard solution sent last week via my e-mail. If you need anything else please let me know.
Thanks, and as you now know, this site was just being launched when you wrote us, so I greatly appreciate your patience as we found your original inquiry & responded to learn more of what was needed for your installation.
Originally posted by Randy B Goodrich - 9 months ago