Hi all,
I'm new to Schneider PLC. I had try some READ VAR tutorial but I couldn't get the data. There are few uncertainty in my mind.
1. When I using M340 with P342020 what is the ethernet and modbus VP 5V5 r.m.c? 0.1.x
2. when I add network for ethernet it is unable to build.
3. What is the code error means for array check[2]?
I not sure what I miss out when configuring.
Early thanks for read and help in my problem.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-16 07:14 AM
your syntax for ADDM is not quite right, you have to use '0.0.3{IP Address}Tcp.mbs'. make sure Data variable array size is the same as NB, see the pictures attached.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-16 07:14 AM
your syntax for ADDM is not quite right, you have to use '0.0.3{IP Address}Tcp.mbs'. make sure Data variable array size is the same as NB, see the pictures attached.