Hello,

Can anyone please tell me how to reset Modicon TM171O or the solution to this proble?

I accidentally changed Modbus settings and now it's not connecting to the software.

Thanks in Advance!

@plc

Tags (1)

Accepted Solutions
Bastian_Schmitz
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
312

Re: TM171 Factory Reset

The easiest way should be to check the modbus parameters via the local display. If you did not have the local display you could use TM171DLED.

To check the configuration you need to enter the BIOS menue.

biosmenue.PNG

biosmenue2.PNG

See Answer In Context

Tags (1)
1 Reply 1
Bastian_Schmitz
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
313

Re: TM171 Factory Reset

The easiest way should be to check the modbus parameters via the local display. If you did not have the local display you could use TM171DLED.