MODICON M221 EcoStruxure TIMER

Hello everyone, 

 

I am new to Schneider and EcoStruxure. I am now programming a Modicon M221 with the EcoStruxure Basic Software. It's a simple application that requires a timer, and I want to be able to change the PRESET value through an HMI. I was only able to find a TIMER block that allows an input to start the timer, a fixed PRESET value, and an output Q. 
Is it possible to make the PRESET a variable and change that variable through the HMI?

 

Thank you in advance for your time. 

 

 

Tags (5)
2 Replies 2
Bastian_Schmitz
Lt. Commander Lt. Commander
Lt. Commander

Re: MODICON M221 EcoStruxure TIMER

Hello,

You can reach your goal on the follow way.

You can write a variabel (as example %MW0 which is reachable via Modbus) in the instance of the Timer.

If you use %TM*.P you can overwrite the preseted Time value. (* = number of timer)

 

mm2.PNG

 

best regards

Tags (1)
Sanzio94
Crewman
Crewman
0 Likes
0
645

Re: MODICON M221 EcoStruxure TIMER

Thank you, much appreciated. 