Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
80616members
346561posts

MODICON M221 EcoStruxure TIMER

Sanzio94
Crewman
Crewman

MODICON M221 EcoStruxure TIMER

Hello everyone, 

 

I am new to Schneider and EcoStruxure. I am now programming a Modicon M221 with the EcoStruxure Basic Software. It's a simple application that requires a timer, and I want to be able to change the PRESET value through an HMI. I was only able to find a TIMER block that allows an input to start the timer, a fixed PRESET value, and an output Q. 
Is it possible to make the PRESET a variable and change that variable through the HMI?

 

Thank you in advance for your time. 

 

 

Tags (5)
2 Replies 2
Bastian_Schmitz
Lt. Commander Lt. Commander
Lt. Commander

Re: MODICON M221 EcoStruxure TIMER

Hello,

You can reach your goal on the follow way.

You can write a variabel (as example %MW0 which is reachable via Modbus) in the instance of the Timer.

If you use %TM*.P you can overwrite the preseted Time value. (* = number of timer)

 

mm2.PNG

 

best regards

Tags (1)
Sanzio94
Crewman
Crewman
0 Likes
0
644

Re: MODICON M221 EcoStruxure TIMER

Thank you, much appreciated. 

Tags (1)