Modicon PAC Forum
A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-06-23 06:19 AM
Hello all,
In one of our Project client requested to include PLC( M580 Hot standby) internal battery low alarm status which is to be configured in PLC/SCADA.
is there maybe a system bit to monitor the battery state of the M580, knowing that M580 has no internal battery..
Is it possible or not ?
Isra
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-06-23 02:20 PM
1. The M580 does not rely on a battery for memory backup so there is nothing to monitor.
2. They can monitor the status of the M580 CPU and HSBY functionality via the Device DDT.
3. The Redundant Power Supplies when mounted in a BMEXBP0602 or BMEXBP1002 rack can provide diagnostic from each power supply. NOTE: This only applies to the primary rack
4. The status of all I/O can be monitored vis the associated Device DDT.
5. I would use the Schneider Electric OPC-DA or OPC-US server to directly read the unlocated variables in the Modicon Quantum controller.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-06-23 02:20 PM
1. The M580 does not rely on a battery for memory backup so there is nothing to monitor.
2. They can monitor the status of the M580 CPU and HSBY functionality via the Device DDT.
3. The Redundant Power Supplies when mounted in a BMEXBP0602 or BMEXBP1002 rack can provide diagnostic from each power supply. NOTE: This only applies to the primary rack
4. The status of all I/O can be monitored vis the associated Device DDT.
5. I would use the Schneider Electric OPC-DA or OPC-US server to directly read the unlocated variables in the Modicon Quantum controller.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 3 weeks ago
Hi Rob,
I am trying to read my M580 operating state with OPC-DA, just not sure what data type to use for reading it and if it needs decoding. Do you have any resource for this information?
Ronan
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.