Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
80616members
346561posts

How to local manual override of Digital/Analog output card without CPU

Samart_Ploypradab
Ensign Ensign
Ensign
0 Likes
1
358

How to local manual override of Digital/Analog output card without CPU

Dear Friend 

 

I got some question from my customer about in emergency case, The CPU card fail of dead.

Can manual send command directly to DO/AO card via CRA with unity pro or relate software?

 

It's possible or not?

 

Thank you for advance.

1 Reply 1
AlastairF
Lieutenant Lieutenant
Lieutenant
0 Likes
0
355

Re: How to local manual override of Digital/Analog output card without CPU

What is the issue with the CPU?

Any LED's active?

 

Not easy (almost impossible) to force IO modules in a remote rack without a CPU. The CRA receives the rack configuration from the CPU and then processes the EIP IO communication. And then there are issues around message repeat rate to avoid drop out on slow/ erratic comms.

 

Most likely be quicker to get a replacement CPU if that is available.

We have had customers in this situation and they have used a CPU from a low priority process that they can shut down.