Can we define another TCP port for Modbus TCP request?

Hello,

 

I would like to send request to a Modbus TCP/IP slave but on port 503 instead of the standard Modbus TCP 502 port.

 

I saw the stucture of the ADDMX string is like that ‘r0.s0.ch0{ip.ip.ip.ip}TCP.MBS\\r1.s1.ch1.d.MBS.

Is there any way to used someting different than TCP.MBS when using a Read_Var bloc?

 

Maybe it is possible with other type of bloc...

 

Thank you

 

PS: I have an M580 CPU and a NOC0301 board.

Tags (1)
1 Reply 1
SEStig
Crewman Crewman
Crewman
0 Likes
0
66

Re: Can we define another TCP port for Modbus TCP request?

Yes, you definitely can, although I don’t think natively out of an addmx block. If you look at the resultant data out of an addmx block set for the read_var or write_var on normal modbus TCP you will see the port 502 in one of the array entries (off the top of my head it might be entry 6 or 7). From that you could just make a block to write into the ADDR type with the info directly, removing the need for the ADDMX block in this scenario.