Posted: 2021-09-11 05:55 AM
Is it possible to connect Modbus TCP device to BMECRA31210 Service Port?
Posted: 2021-09-12 09:19 PM
Definitely yes.
Outlined in this manual in a number of places.
This Service port is not restricted to MBTCP communications.
Posted: 2021-09-12 09:19 PM
Definitely yes.
Outlined in this manual in a number of places.
This Service port is not restricted to MBTCP communications.
Posted: 2021-10-05 09:09 AM
How to add Modbus TCP device to BMECRA31210 service port?
Posted: 2021-10-05 09:14 AM
What type of device are you trying to add?
Posted: 2021-10-05 09:17 AM
PLC - Carel pCO3 with Modbus TCP extension card.
Posted: 2021-10-05 09:38 AM
Hello,
Modbus TCP devices connected to the Service port of BME CRA are added in the DTM Browser.
It is the scanner of the CPU who is used, no BME NOC required.
This Scanner can Manage 61 Devices for CPU xx40 Modele.
The MBTCP Device must be adressed with the same IP Adresse as the CPU IP Adress A.
To add a device, open the DTM Browser, right clic on the CPU and ADD a device.
BR