Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Link copied. Please paste this link to share this article on your social media post.
Hello,
I'm using an ION9000 and I'm setting up some data recorders using Designer tool.
I can find easily core registers (like I, U, kW...) in Power Meter Modules or HS Power Meter Module but I don't know where I can find some registers appearing in the modbus table. For sure if these registers exist in the Modbus table, they must be accessible inside Designer.
For instance, if I want to connect this register to a data recorder
where do I find this register in Designer ?
Thank you very much for you help
Link copied. Please paste this link to share this article on your social media post.
I believe it is in the Symm Comp core modules - "I Symm Comp"
Link copied. Please paste this link to share this article on your social media post.
I believe it is in the Symm Comp core modules - "I Symm Comp"
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.