Hello
is there someone how can provide the register list of the PM5100/PM5300 series with the energy values in Float32?
Thanks a lot
Hi Jeroen,
The register lists for PM5100/5300 are available on the Schneider website - http://www2.schneider-electric.com/resources/sites/SCHNEIDER_ELECTRIC/content/live/FAQS/234000/FA234...
Each energy value is held in 4 X 16-bit registers, so the format to read an energy value is in INT64. It will not be possible to read the register in Float32 format, not unless you read the raw data from each register and reconstruct this, but there's a fair amount of 'reinventing the wheel' involved.
What are you trying to do?
Regards.
In the new Firmware V01.4.7 the added the Float32 energy readings....
Gotcha! Didn't know that. I've had a search also and couldn't find an updated register list. If I find anything I'll put it on here.
Kind regards.
Hi Jeroen,
The Energy values in Float32 format available in the register list starting from 2700 registers.
Please refer the below path for register list.
PM53xx (PM5310,PM5320,PM5330,PM5331 | Download Schneider Electric
Regards,
Ramasamy.N