Here is a screen capture of what we are reading for one of the iem3555 meters at a site.
Note that current A is a significantly higher than B or C ampere readings and the kW is negative.
Does anyone have a guess on why this would be? All that I can come up with is either a bad sensor, the wrong sensor type on that phase or a problem with the meter itself.
Has anyone else witnessed this issue?
Sincerely,
Michael Franz l APC
Technical Consultant
Link copied. Please paste this link to share this article on your social media post.
Check wiring.
Link copied. Please paste this link to share this article on your social media post.
Yut:
Our electricians have checked the wiring. I would suspect that if "A” were
backwards then it would read close to the rest in a balanced system but be
negative.
Here we are negative and over 40 times different than the other phases.
We believe that it is a malfunctioning sensor that is causing the issue.
Sincerely,
Michael