Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Link copied. Please paste this link to share this article on your social media post.
Device name
->PM8240
Communication Method
->Modbus TCP only
At the user site SI team question me, how to reset kwh value using only Modbus tcp protocol
Before I was check Modbus map it but kWh parameter can't reset.
Otherwise I can do it, PME handle easily but there user can’t it
Please give me good idea?
Link copied. Please paste this link to share this article on your social media post.
In general for ION meter the master reset is external pulse number 19(ep19) Modbus address is 42019 try it.
Link copied. Please paste this link to share this article on your social media post.
External Pulse Module #19 is the Master Reset in the default framework. It's output can be toggled via Modbus at address 52019 (write a 1 to address 52019). Modbus Map Access in the Security Options Module must be set to Yes to enable this functionality.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.