can IONsetup be used to read/display harmonics up to the 50th ?
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Then you would copy one of the standard table viewers instead (ex. Realtime.PML) and open it up in Notepad.
Decide on what type of layout you want to create and determine which handles you need to retrieve (this can be done by either using the Advanced ION module view and examining the ION handles for whatever reading you are wanting to display or getting a list of available ION handles for the firmware you have if available).
Each "cell" in the table view, will likely be of the form:
R#C#=Addr,Format,Decimals,Label
ex. R2C2=0x5803,0,3,Volts LN Avg
Simply replace the Addr shown with the ION handle for each output you wish to show:
ex. R2C2=0x5902,0,3,V1 HD 3
would show the V1 3rd Harmonic value for the V1 Harmonics module.
You would likely need to change R#C1 values to change the displayed label shown down the first column (the one for each cell is not shown and is just a placeholder comment presently) and possibly the R1C# entries to change the column headings across the top.