Hi, of this families... may someone confirm me, if they support or no 200Vac/400Hz ?
PM1000
PM700
PM800
PM5000
PM8000
ION7400
ION7650
ION8650
best regards
Link copied. Please paste this link to share this article on your social media post.
Just to clarify - Neither the PM8000 nor the ION7400 are rated to be powered at 200VAC 400Hz (120VAC is max for safety ratings at 400Hz).
However, both models can measure 200VAC at 400Hz. Most power quality parameters will not function above 70Hz (harmonics, flicker, etc). I believe all the ION meters also have these restrictions & limitations.
Gregory Lado - I'm curious what is the application?
Thanks
Dan
Link copied. Please paste this link to share this article on your social media post.
no one answered this and it's a shame since I have the same question today.
Link copied. Please paste this link to share this article on your social media post.
Hi Jorge, and Gregory,
My apologies for not seeing this earlier. Digging a bit into this, it appears that I can confidently say the PM8000 and the ION7400 support the range specified. However, the accuracy spec is not defined for this the 400Hz frequency, unfortunately. The accuracy spec is only defined for 42 Hz to 69 Hz range.
Best Regards,
Sanjeet
Link copied. Please paste this link to share this article on your social media post.
Just to clarify - Neither the PM8000 nor the ION7400 are rated to be powered at 200VAC 400Hz (120VAC is max for safety ratings at 400Hz).
However, both models can measure 200VAC at 400Hz. Most power quality parameters will not function above 70Hz (harmonics, flicker, etc). I believe all the ION meters also have these restrictions & limitations.
Gregory Lado - I'm curious what is the application?
Thanks
Dan
Link copied. Please paste this link to share this article on your social media post.
From the users manual, PM800, CM2000, CM3000, CM4000 can monitor 400Hz power system, which could be seen in military application