Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Posted: 2021-01-14 06:27 AM . Last Modified: 2024-01-30 05:08 AM
Link copied. Please paste this link to share this article on your social media post.
if i use PM5560 daisy chain to connect many PM5560 maybe 2 or 3 . and i want to test the commuication performence (response time in 1s)
how can i do ?
schneider have this test software or caculation tools ? thank you
Link copied. Please paste this link to share this article on your social media post.
We have tested up to 5 meters in daisy chain connection with the polling interval of 1 second.
However, the general practice for the polling interval of PM5560 will be configured as 5 seconds since the data update time is 1 second.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
We have tested up to 5 meters in daisy chain connection with the polling interval of 1 second.
However, the general practice for the polling interval of PM5560 will be configured as 5 seconds since the data update time is 1 second.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.