Hi people,
We have an application in Brazil that use an voltage of 1500Vdc for Solar Plant and our product (HV1700) is limited in a 1000Vdc. Anybody knows if is possible to use a voltage coupler of the Bender (AGH150W-4)?
Regards...
Link copied. Please paste this link to share this article on your social media post.
Hi,
Voltage adaptors are designed to work with their associated IMDs, and it is not possible to mix the products. For instance, voltage adaptor IM400-1700 works with IM400, only. Be informed that we are working at having such adaptor up to 1500VDC by the end of 2015.
Regards