HI all,
I want reset Energy Value (E Del) to 0 KWh in PM5350. How do I do that?
Thanks all,
Link copied. Please paste this link to share this article on your social media post.
Hi Ta Cong,
Resetting only Energy value (E Del) is not possible in PM5350. The reset command will reset All Accumulated Energies.
Link copied. Please paste this link to share this article on your social media post.
Hi Ramasamy,
Yes. I want reset all energies value.
Link copied. Please paste this link to share this article on your social media post.
Hi Ta Cong,
The Energy reset in PM5350, can be done through Meter HMI by navigating Maint-->Reset--> Single Resets-->Energy or using ION setup --> Meter Resets. Also in PME vista page the reset option is available.