Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Link copied. Please paste this link to share this article on your social media post.
Hi all,
We have a customer is using our power meters PM710 (firmware version 2.0 - 3.0). The contractor had installed wrong CT ratio so that we need to support them. The problem here that they had changed the password (default password is 0000).
So please support to let us know how to recover password (update firmware or we have master password).
Thanks so much your support.
Link copied. Please paste this link to share this article on your social media post.
Hi Tran Bao,
No, unfortunately it seems that backdoor passwords for PM700 with versions that are less than V3.04 are not supported. But try to contact the technical support, maybe they can provide you another solution.
Link copied. Please paste this link to share this article on your social media post.
Hi Tran Bao,
If firmware is V3.040 or higher, then I can provide you a backdoor password. For this I need the serial number of the related PM.
Regards
Daniel
Link copied. Please paste this link to share this article on your social media post.
Hi Daniel,
They have around 40 PM710. They have both firmware v.2.02 and 3.04. Do you have any solution with v.2.02?
Thanks so much your support.
Link copied. Please paste this link to share this article on your social media post.
Hi Tran Bao,
No, unfortunately it seems that backdoor passwords for PM700 with versions that are less than V3.04 are not supported. But try to contact the technical support, maybe they can provide you another solution.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.