Can a power meter with transient detection detect transients which have a duration less than the sample time? E.g. ION7650 can detect 20us transients and has a sample rate of 256/cycle.
Link copied. Please paste this link to share this article on your social media post.
The ION7650 comes standard with 512 samples/cycle or optional 1024 samples/cycle.
Impulse transients shorter than a sample period may sometimes be detected - if the sample aquisition happens to coincide with the transient event. The meter always reports transient durations in multiples of sample periods.
Link copied. Please paste this link to share this article on your social media post.
The ION7650 comes standard with 512 samples/cycle or optional 1024 samples/cycle.
Impulse transients shorter than a sample period may sometimes be detected - if the sample aquisition happens to coincide with the transient event. The meter always reports transient durations in multiples of sample periods.
Link copied. Please paste this link to share this article on your social media post.
Thanks Dan.
(Australian Catalogue 2013/2014 incorrectly has the ION7650 as 256 samples/cycle).