Hi there,
I'm curios to know, if there is a way to display the waveform captures from PM850/PM870 devices with ION-Setup or if it is only used to configure them?
Will I have to use PMCU for do this, as it was the case in the past?
Thanks
Daniel
Link copied. Please paste this link to share this article on your social media post.
ION Setup still does not allow users to view waveforms produced by any of the older CM/PM PowerLogic devices yet. A future version *may* have that capability but as of right now, you would need to use PME or PMCU/SMS to view those waveforms.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Is the ION SETUP "new version" (able to view WFC) available now ?
Link copied. Please paste this link to share this article on your social media post.
Waveform viewing of older legacy PowerLogic devices hasn't been fully added as of yet. This is still being worked on when I have time available but is on a lower priority than all new development. If this feature does become available, I will definitely let people know about it via a post.