Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
80616members
346561posts

PM8240 Show Blank screen with red/green blinking LED status after connect with RJ45

Solved
Samart_Ploypradab
Ensign Ensign
Ensign
0 Likes
7
378

PM8240 Show Blank screen with red/green blinking LED status after connect with RJ45

The PM8240 4pcs at one of pumping station, when we connect Power Meter via Ethernet LAN cable, the screen of PM8240 is showed blank screen. but when we disconnect Ethernet LAN the screen back to normal use.


We think this problem it maybe come from Ethernet router. So, we checked the ethernet connection other station but the connection of other station is like with this station and it didn’t have this issue.

 

Note: We tried to reset the meter but it still has issues.

 

Video Link "https://mega.nz/file/ddxQlaSY#VXGD_NfI-FMbAfVUYsf9nGN3gnS_r4JozqIZPqieDh0"

Tags (1)

Accepted Solutions
Charles_Murison
Picard Picard
Picard
0 Likes
4
337

Re: PM8240 Show Blank screen with red/green blinking LED status after connect with RJ45

Hello @Samart_Ploypradab ,

 

Strongly recommend you look at putting some filtering at the switch level where meter connected.

 

If you want to troubleshoot with technical support likely they will, if not already, ask for a packet capture of the traffic going to and from the meter. This would need a computer with packet capture software like WireShark running and a switch configured such that the traffic on the port connected to the meter will also be sent to a second port where computer attached, sometimes referred to a port mirror or port forwarding.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
7 Replies 7
Charles_Murison
Picard Picard
Picard
0 Likes
6
364

Re: PM8240 Show Blank screen with red/green blinking LED status after connect with RJ45

Hello @Samart_Ploypradab 

 

I cannot see the video so I cannot speak to anything specific. If you connect directly from laptop to meter does the meter behave in the same way? What version of firmware on the meter? If not the latest does upgrading the meter to the latest help?

 

The PM8000 has mechanisms to protect the metering functionality if the meter sees too much network traffic. I would not expect this traffic to reset a meter but something to look into. Is the network switch configured to only send packets to meter if broadcast or specifically addressed to meter?

 

If you want further troubleshooting recommend working with your local technical support.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
Samart_Ploypradab
Ensign Ensign
Ensign
0 Likes
5
341

Re: PM8240 Show Blank screen with red/green blinking LED status after connect with RJ45

Hello @Charles_Murison 

 

Thank you for your reply. We have contact with local support already.

 

The P8000 can show a display (no issues) after being directly connected to a laptop. 

 

 

Meter information
1. The S/N is ME-2009A976-02
2. Firmware version : 003 000 000

 

Best regards

Attachments
Tags (1)
Charles_Murison
Picard Picard
Picard
0 Likes
4
338

Re: PM8240 Show Blank screen with red/green blinking LED status after connect with RJ45

Hello @Samart_Ploypradab ,

 

Strongly recommend you look at putting some filtering at the switch level where meter connected.

 

If you want to troubleshoot with technical support likely they will, if not already, ask for a packet capture of the traffic going to and from the meter. This would need a computer with packet capture software like WireShark running and a switch configured such that the traffic on the port connected to the meter will also be sent to a second port where computer attached, sometimes referred to a port mirror or port forwarding.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
Samart_Ploypradab
Ensign Ensign
Ensign
0 Likes
3
264

Re: PM8240 Show Blank screen with red/green blinking LED status after connect with RJ45

Hello @Charles_Murison 

 

We have contact with the local team already, but I let the customer get the WireShark log file as per your recommendation.

 

Kindly help me check this log. Thank you in advance.

 

We tested three more times.

 

Connect to the network switch for the first time at 15.47.

Connect to the network switch for the second time at 15.57.

Connect to the network switch for the third time at 16.07

 

Please find attached the file you requested.

Tags (1)
Samart_Ploypradab
Ensign Ensign
Ensign
0 Likes
0
261

Re: PM8240 Show Blank screen with red/green blinking LED status after connect with RJ45

 
Tags (1)
Charles_Murison
Picard Picard
Picard
0 Likes
1
251

Re: PM8240 Show Blank screen with red/green blinking LED status after connect with RJ45

Hello @Samart_Ploypradab ,

 

From the first Wireshark alone I can say that the switch is not configured well. There is way more network traffic that does not apply to the meter being recorded. Really, really recommend configuring the switch to limit traffic to just the PM8000 (and any meters downstream is Ethernet is daisy chained). 

 

Please delete the Wireshark files from you post. I doubt customer would like anybody on the internet having such details on their system.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
Samart_Ploypradab
Ensign Ensign
Ensign
0 Likes
0
242

Re: PM8240 Show Blank screen with red/green blinking LED status after connect with RJ45

@Charles_Murison

Thank you for your reply. I will let them re-configure the Ethernet switch.

 

Note: I've already deleted all the log files and videos.

Tags (1)