Hello everyone,
It’s our pleasure to announce that we have officially released the PM8000 V2 firmware! As a reminder, this firmware update is bringing the following main features:
The firmware files and "what's new" document is available in the "Firmware Releases" community space.
The PM8000 guidebook is being updated with the new tehnical and marketing documentation to support this release. Please allow us until early next week to finish this task.
Please let me know if any questions. We count on you to keep growing the Advanced Metering business!!
Daniel
Link copied. Please paste this link to share this article on your social media post.
Hello Daniel,
I didn't find the download for V2 ?
Can you please send me the download link?
Thank you
Link copied. Please paste this link to share this article on your social media post.
Hi Sven,
The actual firmware version is 1.4.1, The V2 naming came out as a second major release of meter functionalities. All the new features are described on Daniel's posting and the What's new document on the page you just highlighted.
Please let us know if you have any issue downloading or using the new firmware release.
Fabricio
Link copied. Please paste this link to share this article on your social media post.
Updated user guide here: https://www.schneider-electric.us/en/download/document/7EN02-0336/
Firmware files can also be found here: https://www.schneider-electric.com/en/download/document/PM8000_V001.004.001/
Link copied. Please paste this link to share this article on your social media post.
Additional techdoc updates for this release:
What’s new in PM8000 series firmware v1.4.1 | Schneider Electric
Link copied. Please paste this link to share this article on your social media post.
Hello Sorry what is the difference between meter framework510 and PQ ?
An which one should I use?
Why is all the meter data deleted with the firmware upgrade?
Link copied. Please paste this link to share this article on your social media post.
Hi Sven,
You should probably contact Technical Support so they can help you.
Link copied. Please paste this link to share this article on your social media post.
I do have a case since last year:
Link copied. Please paste this link to share this article on your social media post.
Hi Sven - the 519 framework would be used if you want to utilize the "Harmonics Compliance" report in PME. It does IEEE519 at the expense of EN50160, however, so if you need the latter, use the PQ framework (and the default one).
Meter data is not persisted upon a firmware upgrade, hence the recommendation to ensure your logs are caught up prior to the upgrade.
Tom
Link copied. Please paste this link to share this article on your social media post.
Hi Sven,
as we could find out last friday. the Problem was that the Pm8000 was not configured properly.
As is remotely change only two settings we got the PM8000 working.
It was your mistake.
Link copied. Please paste this link to share this article on your social media post.
very productive input - thank you Abdelatif
Link copied. Please paste this link to share this article on your social media post.
I can't seem to find the .dcf files.
Is there a link?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
The DCFs are embedded in the firmware zip file in the links in Daniel Brandao's post above.
Otherwise you can use the following link:
https://schneider-electric.box.com/v/IonSetup
Most DCFs should be available in the ION Templates sub-folder and if there are additional ones you need uploaded, let me know.
Link copied. Please paste this link to share this article on your social media post.
Hello,
I am monitoring this link for any new ION meter firmware release:
https://schneider-electric.app.box.com/v/IONFirmware/folder/1251922932
I found out from my colleague here that the PM8000 V2.1.0 is now released and can be found here:
Would be good if we have one location for all firmwares and maybe announce it here in the commuinity if there is a new one.
Anyway, we see in "What's New?" that there is a lot of enhancements in this firmware. Good job team!
Regards,
Arneil
Link copied. Please paste this link to share this article on your social media post.
Thanks for the feedback Arneil. We are currently looking at improving this aspect and your feedback is valuable as a consumer of this information. Our current plan is that we would package FW releases with the associated documentation and post on SE.com. We would then announce via the Exchange Community to point to the latest release. If you have recommendations on this please let us know.