I have a customer here who has some PM8000 meters, they would like to read the HS values from the modbus registers shown below.
In Demo mode these do not seem to update any faster than 1 second.
Has anyone tried this before? and do you get a much faster update of the registers.
Thanks
HS Current A | 21000 | 2 | FLOAT32 | A | R/O | numeric | --- | HS I a | CT_A | MEM | None | |
HS Current B | 21002 | 2 | FLOAT32 | A | R/O | numeric | --- | HS I b | CT_A | MEM | None | |
HS Current C | 21004 | 2 | FLOAT32 | A | R/O | numeric | --- | HS I c | CT_A | MEM | None | |
HS Current N | 21006 | 2 | FLOAT32 | A | R/O | numeric | --- | HS I 4 | CT_A | MEM | None | |
HS Current G | 21008 | 2 | FLOAT32 | A | R/O | numeric | --- | HS I 5 | CT_A | MEM | None | |
HS Current Avg | 21010 | 2 | FLOAT32 | A | R/O | numeric | --- | HS I avg | CT_A | MEM | None | |
HS Frequency | 21016 | 2 | FLOAT32 | Hz | R/O | numeric | --- | HS Freq | HZ | MEM | None | |
HS Voltage, A-B | 21018 | 2 | FLOAT32 | V | R/O | numeric | --- | HS Vll ab | PT_V | MEM | None | |
HS Voltage, B-C | 21020 | 2 | FLOAT32 | V | R/O | numeric | --- | HS Vll bc | PT_V | MEM | None | |
HS Voltage, C-A | 21022 | 2 | FLOAT32 | V | R/O | numeric | --- | HS Vll ca | PT_V | MEM | None | |
HS Voltage, L-L Average | 21024 | 2 | FLOAT32 | V | R/O | numeric | --- | HS Vll avg | PT_V | MEM | None | |
HS Voltage, A-N | 21026 | 2 | FLOAT32 | V | R/O | numeric | --- | HS Vln a | PT_V | MEM | None | |
HS Voltage, B-N | 21028 | 2 | FLOAT32 | V | R/O | numeric | --- | HS Vln b | PT_V | MEM | None | |
HS Voltage, C-N | 21030 | 2 | FLOAT32 | V | R/O | numeric | --- | HS Vln c | PT_V | MEM | None | |
HS Voltage, L-N Average | 21034 | 2 | FLOAT32 | V | R/O | numeric | --- | HS Vln avg | PT_V | MEM | None |
Link copied. Please paste this link to share this article on your social media post.
Hi Andrew,
You are correct that the HS Power Meter Module only updates once per second in demo mode. With a non-demo volts mode, the data is refreshed every half-cycle.
The caveat with reading this over modbus, is that the round-trip comm delay in making a request and getting a response for highspeed data is variable. Depending on the meter loading it could take up to a second to get a response (metering and logging is always higher priority than comms). You will need to benchmark it in your specific scenario to see if it will be fast enough for your needs.
Link copied. Please paste this link to share this article on your social media post.
Since the are almost in order I guess it would be smart to create a Modbus Register Group that reads all signals at a time
I assumed it was SmartStruxure, but maybe it wasn´t
Christer
Link copied. Please paste this link to share this article on your social media post.
Hi Andrew,
You are correct that the HS Power Meter Module only updates once per second in demo mode. With a non-demo volts mode, the data is refreshed every half-cycle.
The caveat with reading this over modbus, is that the round-trip comm delay in making a request and getting a response for highspeed data is variable. Depending on the meter loading it could take up to a second to get a response (metering and logging is always higher priority than comms). You will need to benchmark it in your specific scenario to see if it will be fast enough for your needs.
Link copied. Please paste this link to share this article on your social media post.
Hi Patrick,
Thanks for the reply, that is exactly as I had hoped.
My customer is redaing the registers from a PLC connected via TCP, so it should be fast enough.
Thanks
Andy