Sign In Help
Schneider Electric
HelpLogin / Register

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Communities
  • :
  • EcoStruxure Power & Grid
  • :
  • Metering & Power Quality
  • :
  • PM8000 Firmware Issue
Community Menu
  • Forums
    • By Topic
        • EcoStruxure Building
          • Field Devices Forum
        • EcoStruxure Power & Grid
          • Metering & Power Quality
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Automation Forum
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
          • Motorabgangstechnik & Antriebstechnik Forum
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Solutions for Motor Management
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
          • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
        • Power Distribution NEMA
          • US Utility Forum
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure Building
        • Field Devices Forum
      • EcoStruxure Power & Grid
        • Metering & Power Quality
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Automation Forum
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
        • Motorabgangstechnik & Antriebstechnik Forum
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Solutions for Motor Management
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
        • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Power Distribution NEMA
        • US Utility Forum
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • EcoStruxure Power & Grid
          • Backstage Access Resources
        • Industrial Automation
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
          • UK&I Residential and Commercial Electrical Distribution
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
          • Solutions for eMobility
          • Digital Hospital Solutions – UK&I
        • Knowledge Center
          • Industrial Automation How-to videos
          • Digital E-books
          • Success Stories Corner
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
        • Retail
          • Solutions for eMobility
        • Retail
          • Digital Hospital Solutions – UK&I
      • EcoStruxure Power & Grid
        • Backstage Access Resources
      • Industrial Automation
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
        • UK&I Residential and Commercial Electrical Distribution
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
        • Solutions for eMobility
        • Digital Hospital Solutions – UK&I
      • Knowledge Center
        • Industrial Automation How-to videos
        • Digital E-books
        • Success Stories Corner
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
      • Retail
        • Solutions for eMobility
      • Retail
        • Digital Hospital Solutions – UK&I
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Register Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
53099members
248513posts

PM8000 Firmware Issue

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to Metering & Power Quality
Solved
solutions_iems-
Lieutenant solutions_iems-
Lieutenant
‎2019-05-03 07:56 AM
0 Likes
27
633
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-05-03 07:56 AM

PM8000 Firmware Issue

I have a hands-on customer who has tried to upgrade the firmware in a PM82401 to v2.1 to enable waveforms to be viewed in the device web pages. Unfortunately, it has not worked and whatever has been done has affected the framework in the meter so it no longer displays all data in the web pages and 47 modules are off-line when the upgrade has been completed.

 

Fortunately this meter is not fully commissioned yet so is there a way to reset the meter to factory default so that he can can start over?

 

I have attached the screen captures taken from the upgrade.

 

Thanks

 

Attachments
Share
Reply

Accepted Solutions
Cliff_Schubert
Lieutenant JG Cliff_Schubert Lieutenant JG
Lieutenant JG
‎2019-05-30 09:49 AM
2 Likes
14
579
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-05-30 09:49 AM

Re: PM8000 Firmware Issue

The latest 2.1.0 firmware for the PM8000 MID meter is here:

https://www.schneider-electric.com/en/download/document/PM8000_MID_meter_FW_v2.1.0/

 

With ION Setup v3.1 you can choose the zip file for the upgrade which will allow you to program the meter firmware, web pages, and default template all from the one file.

 

You can upgrade directly from 1.1.0 to 2.1.0 using the zip file referenced above and ION Setup will perform any intermediate upgrades for you.

See Answer In Context

Share
Reply
Robert_Lee
Captain Robert_Lee Captain
Captain
‎2019-06-05 09:19 AM
1 Like
8
544
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-06-05 09:19 AM

Re: PM8000 Firmware Issue

That's the wrong file.  It should be called TEMPLATE.LOG and should be located in the following folder:

C:\ProgramData\Schneider Electric\ION Setup

You might also want to also send us your SYSTEM.LOG file as well.

 

You might try to unzip the Web page zip file to a temporary file location and try to upload those files/folders using a FTP client (like WinSCP/FileZilla or even Windows Explorer).  If you are unable to connect to the FTP port, then its likely blocked by some type of networking equipment which you could try to bypass with a direct cross-over cable directly to the device (you would likely have to reprogram your laptop's IP address to one on the same subnet as the PM8000 at that point).

See Answer In Context

Share
Reply
Cliff_Schubert
Lieutenant JG Cliff_Schubert Lieutenant JG
Lieutenant JG
‎2019-07-08 09:21 AM
2 Likes
1
504
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-07-08 09:21 AM

Re: PM8000 Firmware Issue

That message indicates the meter does not have any web pages loaded. The web page files are provided along with every firmware release. You can upload the meter web pages via FTP or using ION Setup.

 

There are instructions in this thread and also on page 188 in the PM8000 user guide: https://www.schneider-electric.ca/en/download/document/7EN02-0336/

See Answer In Context

Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
27 Replies 27
Charles_Murison
Picard Charles_Murison Picard
Picard
‎2019-05-03 09:26 AM
2 Likes
4
631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-05-03 09:26 AM

Re: PM8000 Firmware Issue

Recommend going from V1.1 to V1.3 first before going to V1.4.3. There were some changes between V1.1 and V1.4.3 that could possibly make the upgrade have challenges. 

 

https://www.schneider-electric.ca/en/download/document/PM8000_V001.003.001.upg/

L4 Prime for Advanced metering and Utilities
Share
Reply
solutions_iems-
Lieutenant solutions_iems-
Lieutenant
‎2019-05-08 03:10 AM
0 Likes
3
621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-05-08 03:10 AM

Re: PM8000 Firmware Issue

Hi

 

I tried the v1.3 upgrade but am still having problems with the RMP framework. What else can I try?

 

Thanks

 

 

Attachments
Share
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard
‎2019-05-08 01:43 PM
0 Likes
0
618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-05-08 01:43 PM

Re: PM8000 Firmware Issue

Recommend making sure you have the latest version of ION Setup, if you do have that, then will need to log a case with technical support. Be sure to include the log files from "C:\ProgramData\Schneider Electric\ION Setup"
Screen shot of the device settings, ION Setup -> select device -> Diagnostics -> General tab would also be a good idea.

L4 Prime for Advanced metering and Utilities
Share
Reply
Tom_Stevenson
Picard Tom_Stevenson Picard
Picard
‎2019-05-09 10:22 AM
0 Likes
1
615
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-05-09 10:22 AM

Re: PM8000 Firmware Issue

What framework version are you trying to RMP to your 1.3.1 firmware device?  (as per your ION Setup screen shot) - wondering if you not trying to get to 2.1.0, then do the RMP piece?

Share
Reply
Tom_Stevenson
Picard Tom_Stevenson Picard
Picard
‎2019-05-15 08:30 AM
0 Likes
21
607
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-05-15 08:30 AM

Re: PM8000 Firmware Issue

@solutions_iems- Just want to confirm you have this resolved - thanks !

 

Tom

Share
Reply
solutions_iems-
Lieutenant solutions_iems-
Lieutenant
‎2019-05-16 02:00 AM
0 Likes
0
602
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-05-16 02:00 AM

Re: PM8000 Firmware Issue

No not yet. Not had the opportunity to try as I'm bogged down with PME software issues at the moment. Thanks

Share
Reply
solutions_iems-
Lieutenant solutions_iems-
Lieutenant
‎2019-05-16 02:15 AM
0 Likes
0
598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-05-16 02:15 AM

Re: PM8000 Firmware Issue

What is the recommended firmware upgrade path from v1.1 to v2.1 and which RMP should be used?

Share
Reply
solutions_iems-
Lieutenant solutions_iems-
Lieutenant
‎2019-05-29 06:46 AM
0 Likes
19
590
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-05-29 06:46 AM

Re: PM8000 Firmware Issue

Hi Tom

 

One PME issue resolved and one pending, so back to the PM8000 FW.

 

The meter is FW v001.001.000 as per attached but is not displaying all live data. What do I need to get this back to a functional device before I even consider upgrading the firmware to display waveforms in the web pages?

 

Thanks

Attachments
Share
Reply
Tom_Stevenson
Picard Tom_Stevenson Picard
Picard
‎2019-05-29 10:53 AM
0 Likes
18
588
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-05-29 10:53 AM

Re: PM8000 Firmware Issue

David Anderson on the firmware team here believes it sounds like an interrupted upgrade - the recommendation is to go to firmware version 1.4.3 first, then proceed with the upgrade to 2.1.0 again.

 

Tom 

Share
Reply
solutions_iems-
Lieutenant solutions_iems-
Lieutenant
‎2019-05-30 01:15 AM
0 Likes
17
585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-05-30 01:15 AM

Re: PM8000 Firmware Issue

I have upgraded the meter to v1.4.3 firmware and it has partially restored the meter functionality (see attached process and errors) but the meter still states that it is v1.1.0 in ION Setup and the Diagnostic web page.

 

I'm guessing that the missing functionality is down to the compatibility of the installed template (v1.4.0) with V1.1.0 firmware?

 

Should I now try upgrading to v2.1?

Attachments
Share
Reply
Tom_Stevenson
Picard Tom_Stevenson Picard
Picard
‎2019-05-30 08:37 AM
0 Likes
16
583
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-05-30 08:37 AM

Re: PM8000 Firmware Issue

Hmmm - it looks like you have a PM8000 MID meter, not a standard PM8000 - can you confirm?  The PM8000 and ION7400 have a different firmware file for MID.  The "NAK Target Not Supported" message is indicating this (wrong firmware file for this device type).  Looking at the messages, the 1.4.3 operation did not work for the same reason - you need the MID firmware.

 

@Cliff_Schubert 

 

 

 

Share
Reply
solutions_iems-
Lieutenant solutions_iems-
Lieutenant
‎2019-05-30 08:40 AM
0 Likes
15
581
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-05-30 08:40 AM

Re: PM8000 Firmware Issue

It is the MID version (METSEPM82401).

 

Do you have a link to the MID F/W upgrade?

 

Thanks

Share
Reply
Cliff_Schubert
Lieutenant JG Cliff_Schubert Lieutenant JG
Lieutenant JG
‎2019-05-30 09:49 AM
2 Likes
14
580
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-05-30 09:49 AM

Re: PM8000 Firmware Issue

The latest 2.1.0 firmware for the PM8000 MID meter is here:

https://www.schneider-electric.com/en/download/document/PM8000_MID_meter_FW_v2.1.0/

 

With ION Setup v3.1 you can choose the zip file for the upgrade which will allow you to program the meter firmware, web pages, and default template all from the one file.

 

You can upgrade directly from 1.1.0 to 2.1.0 using the zip file referenced above and ION Setup will perform any intermediate upgrades for you.

See Answer In Context

Share
Reply
solutions_iems-
Lieutenant solutions_iems-
Lieutenant
‎2019-05-31 01:01 AM
0 Likes
13
571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-05-31 01:01 AM

Re: PM8000 Firmware Issue

Thank you for the link to the upgrade file.

 

I have applied the upgrade and can confirm that it was 100% successful, however...

 

The web pages no longer work! - please see attached for details

Attachments
Share
Reply
Tom_Stevenson
Picard Tom_Stevenson Picard
Picard
‎2019-05-31 08:21 AM
1 Like
12
567
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-05-31 08:21 AM

Re: PM8000 Firmware Issue

That is good news !  For the web pages - just confirming you have the latest ION Setup.  If so, have you tried just re-uploading only the web pages?  In ION Setup, it's under "Template" in the wizard, "Web" tab, and then click the "Upload" button.  Tech support will be able to assist if needed - sounds like you are really close !  

 

If you have the latest ION Setup, can you post the log file here, so we can take a look - thanks !  @Robert_Lee 

Share
Reply
solutions_iems-
Lieutenant solutions_iems-
Lieutenant
‎2019-06-03 09:31 AM
0 Likes
11
556
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-06-03 09:31 AM

Re: PM8000 Firmware Issue

Hi Tom

 

Yes I am using the latest version of ION Setup (v3.1.19095.01) and I have just tried uploading the web pages from the Template "Upgrade" and "Web" tabs but neither has made any difference.

 

Where will I find the ION Setup log file?

 

Thanks

Share
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard
‎2019-06-03 09:40 AM
1 Like
10
553
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-06-03 09:40 AM

Re: PM8000 Firmware Issue

C:\ProgramData\Schneider Electric\ION Setup

 

May also be good to ftp to the meter and get a copy of the web files currently on the device.

L4 Prime for Advanced metering and Utilities
Share
Reply
solutions_iems-
Lieutenant solutions_iems-
Lieutenant
‎2019-06-05 07:30 AM
0 Likes
9
548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-06-05 07:30 AM

Re: PM8000 Firmware Issue

There are no web files on the meter. All folders are empty.

 

Copy of ION Setup log attached.

Attachments
Share
Reply
Robert_Lee
Captain Robert_Lee Captain
Captain
‎2019-06-05 09:19 AM
1 Like
8
545
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-06-05 09:19 AM

Re: PM8000 Firmware Issue

That's the wrong file.  It should be called TEMPLATE.LOG and should be located in the following folder:

C:\ProgramData\Schneider Electric\ION Setup

You might also want to also send us your SYSTEM.LOG file as well.

 

You might try to unzip the Web page zip file to a temporary file location and try to upload those files/folders using a FTP client (like WinSCP/FileZilla or even Windows Explorer).  If you are unable to connect to the FTP port, then its likely blocked by some type of networking equipment which you could try to bypass with a direct cross-over cable directly to the device (you would likely have to reprogram your laptop's IP address to one on the same subnet as the PM8000 at that point).

See Answer In Context

Share
Reply
solutions_iems-
Lieutenant solutions_iems-
Lieutenant
‎2019-06-06 01:08 AM
0 Likes
7
539
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-06-06 01:08 AM

Re: PM8000 Firmware Issue

Template.log and System.log files attached for reference.

 

The great news is that by unzipping and copying the web page files direct to the meter using Windows Explorer and FTP has worked!!!!!!

 

Thank you all for your assistance with this matter 🙂

Attachments
SYSTEM.LOG
TEMPLATE.LOG
Share
Reply
Robert_Lee
Captain Robert_Lee Captain
Captain
‎2019-06-06 08:44 AM
0 Likes
6
535
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-06-06 08:44 AM

Re: PM8000 Firmware Issue

What OS version is running on the PC.  ION Setup is attempting to use PowerShell V3 (which should be available in most newer WIndows OSes), in order to automatically unzip the web zip file but I don't see an entry in the SYSTEM.LOG indicating that the unzip was successful.

 

Thursday, June 6, 2019 8:41:33 AM: UNZIP, Process, powershell.exe "& { Add-Type -A 'System.IO.Compression.FileSystem'; [IO.Compression.ZipFile]::ExtractToDirectory('C:\ProgramData\Schneider Electric\ION Setup\www\ION9000_webpages_000.001.925.zip', 'C:\Users\SESA70~1\AppData\Local\Temp\IONSET~2\web\'); }", Target, C:\Users\SESA70~1\AppData\Local\Temp\IONSET~2\web\

 

Something like the above entry should appear in the SYSTEM.LOG when you attempt to upload web pages clicking on the Upload button from the Web tab and you've selected the zip file (you would also see a dialog appear as it is uploading the individual files *IF* it is successful in unzipping.

Share
Reply
solutions_iems-
Lieutenant solutions_iems-
Lieutenant
‎2019-06-06 09:04 AM
0 Likes
5
532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-06-06 09:04 AM

Re: PM8000 Firmware Issue

Windows Server 2016 Data Center Edition

Share
Reply
jan_opsteyn
Lieutenant | EcoXpert Master jan_opsteyn Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
‎2019-07-08 05:33 AM
0 Likes
4
508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-07-08 05:33 AM

Re: PM8000 Firmware Issue

After upgrading with latest ION software & PM8000 version V002.001.000

Login PM8000.png

Is there a solution to get the web server back?

Share
Reply
Cliff_Schubert
Lieutenant JG Cliff_Schubert Lieutenant JG
Lieutenant JG
‎2019-07-08 09:21 AM
2 Likes
1
505
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-07-08 09:21 AM

Re: PM8000 Firmware Issue

That message indicates the meter does not have any web pages loaded. The web page files are provided along with every firmware release. You can upload the meter web pages via FTP or using ION Setup.

 

There are instructions in this thread and also on page 188 in the PM8000 user guide: https://www.schneider-electric.ca/en/download/document/7EN02-0336/

See Answer In Context

Share
Reply
solutions_iems-
Lieutenant solutions_iems-
Lieutenant
‎2019-07-08 09:50 AM
0 Likes
0
501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-07-08 09:50 AM

Re: PM8000 Firmware Issue

The issue is now resolved.

 

The PM8000 meter was the MID version but the firmware was for the non-MID version.

 

Once upgraded with the correct version (MID), the firmware upgrade to v2.1 was successful and the web pages and waveforms now all work correctly.

 

Thank you.

Share
Reply
Tom_Stevenson
Picard Tom_Stevenson Picard
Picard
‎2019-07-22 02:54 PM
0 Likes
1
475
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-07-22 02:54 PM

Re: PM8000 Firmware Issue

You can try to upload just the web pages again using ION Setup or an FTP client - have your tried this?

 

Thanks


Tom

Share
Reply
jan_opsteyn
Lieutenant | EcoXpert Master jan_opsteyn Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
‎2019-07-22 11:00 PM
0 Likes
0
468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-07-22 11:00 PM

Re: PM8000 Firmware Issue

Webpages are solved. 

uploaded by FTP the files.

 

Thanks

Share
Reply
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
143
Robert_Lee
Captain Robert_Lee Captain
56
Ramasamy_N
Commander Ramasamy_N Commander
40
DanL
Lt. Commander DanL Lt. Commander
31
Nedjma
Nedjma Community Alumni (Retired)
24
Daniel_Brandao
Lt. Commander Daniel_Brandao Lt. Commander
17
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2021, Schneider Electric