Is it possible to delete past alarm history from PM8000 meter?
If I Acknowledge Alarm for PM8000 in Power Monitoring Expert, can I make Alarm Acknowledge applied to PM8000 Local Device? (automatically applied)
Best Regard.
Link copied. Please paste this link to share this article on your social media post.
It's worth noting that the term "Alarms" in the context of PME is a separate and distinctly different list from the "Alarms" visible only on the front panel display of the PM8000.
The list of "Alarms" visible in PME are maintained in the PME database and are (mostly) comprised of downloaded EventLog entries from the PM8000 (and the EventLogs of other devices connected to PME).
The list of "Alarms" visible on the front panel display of the PM8000 is a list separate and distinct from the meter's EventLog (though most Alarms usually have one or more corresponding Event entries). The list of "Historical Alarms" and "Active Alarms" visible only on the PM8000 display can only be acknowledged via the display interface on the respective screen.
The list of "Alarms" visible in the PME database can only be acknowledged with PME.
Link copied. Please paste this link to share this article on your social media post.
Hello @Hyeontae-Song ,
To your second question, "can I make Alarm Acknowledge applied to PM8000 Local Device?" The answer is no.
The first question about "delete past alarm history" is a loaded question. The event log on a meter can be cleared, the front panel alarm log cannot. Easiest way to clear a meter's event log is to change the depth, changing this number will clear the log.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
It's worth noting that the term "Alarms" in the context of PME is a separate and distinctly different list from the "Alarms" visible only on the front panel display of the PM8000.
The list of "Alarms" visible in PME are maintained in the PME database and are (mostly) comprised of downloaded EventLog entries from the PM8000 (and the EventLogs of other devices connected to PME).
The list of "Alarms" visible on the front panel display of the PM8000 is a list separate and distinct from the meter's EventLog (though most Alarms usually have one or more corresponding Event entries). The list of "Historical Alarms" and "Active Alarms" visible only on the PM8000 display can only be acknowledged via the display interface on the respective screen.
The list of "Alarms" visible in the PME database can only be acknowledged with PME.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.