Sign In Help
Schneider Electric
HelpLogin / Register

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Communities
  • :
  • EcoStruxure Power & Grid
  • :
  • Metering & Power Quality
  • :
  • PM5560 - reasons for disconnection from Ethernet network
Community Menu
  • Forums
    • By Topic
        • EcoStruxure Building
          • Field Devices Forum
        • EcoStruxure Power & Grid
          • Metering & Power Quality
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Automation Forum
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
          • Motorabgangstechnik & Antriebstechnik Forum
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Solutions for Motor Management
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
          • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
        • Power Distribution NEMA
          • US Utility Forum
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure Building
        • Field Devices Forum
      • EcoStruxure Power & Grid
        • Metering & Power Quality
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Automation Forum
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
        • Motorabgangstechnik & Antriebstechnik Forum
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Solutions for Motor Management
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
        • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Power Distribution NEMA
        • US Utility Forum
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • EcoStruxure Power & Grid
          • Backstage Access Resources
        • Industrial Automation
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
          • UK&I Residential and Commercial Electrical Distribution
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
          • Solutions for eMobility
          • Digital Hospital Solutions – UK&I
        • Knowledge Center
          • Industrial Automation How-to videos
          • Digital E-books
          • Success Stories Corner
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
        • Retail
          • Solutions for eMobility
        • Retail
          • Digital Hospital Solutions – UK&I
      • EcoStruxure Power & Grid
        • Backstage Access Resources
      • Industrial Automation
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
        • UK&I Residential and Commercial Electrical Distribution
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
        • Solutions for eMobility
        • Digital Hospital Solutions – UK&I
      • Knowledge Center
        • Industrial Automation How-to videos
        • Digital E-books
        • Success Stories Corner
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
      • Retail
        • Solutions for eMobility
      • Retail
        • Digital Hospital Solutions – UK&I
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Register Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
53084members
248454posts

PM5560 - reasons for disconnection from Ethernet network

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to Metering & Power Quality
Solved
swil
Lt. Commander swil
Lt. Commander
‎2020-04-21 03:34 AM
0 Likes
5
66
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-04-21 03:34 AM

PM5560 - reasons for disconnection from Ethernet network

Hi,

 

A method to stop random Ethernet Power meters in an Ethernet meter string from disconnecting from the network is sought.

 

Between the roof of a building and the basement is 13-off  PM5560 meters, connected together by Ethernet cable. These meters then connect to a PM8000 by Ethernet cable and back to a network switch and (PME) EMS server. Each power meter except the one at the end of the run (on the roof)  is used as an Ethernet switch for the next power meter.

 

Communication parameters in the PM5560 meters are correct (fixed IP addresses, gateway, subnet mask). Different meters in the Ethernet string, at different times, have stopped communicating with the EMS server, while upstream and downstream meters have maintained their connection to the network. The fix has been to power cycle the meters.

 

Sometimes PM5560 meters can lose their IP addresses. In this case of non-communicating PM5560 meters, fixed IP addresses are retained. Non-communicating meters can't be pinged by the EMS server until they are power cycled.

 

There are several questions regarding the explanation provided above:

1. What may be causing the problem explained?

2. Is there a limit to the number of Schneider Ethernet meters that can exist on a Cat6a Ethernet string?

3. How can I stop this from happening?

4. If the IT department was to power cycle the switch periodically (eg. once a day or every few days), would this force all devices back online?

Share
Reply

Accepted Solutions
Ramasamy_N
Commander Ramasamy_N Commander
Commander
‎2020-04-28 09:56 AM
0 Likes
1
47
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-04-28 09:56 AM

Re: PM5560 - reasons for disconnection from Ethernet network

Hello @swil 

 

Can you please share the following data in mail to analyze this issue?

 

1.Communication network topology. Highlight the effected PM5560 in the diagram. 

2.What is firmware version of PM5560.

3.Copy and share the system.log file (from fw folder in FTP) from PM5560 meters.

 

Regards, 

Ramasamy N 

See Answer In Context

Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
5 Replies 5
tcrawford_marco
tcrawford_marco
Cadet
‎2020-04-21 09:31 AM
0 Likes
1
60
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-04-21 09:31 AM

Re: PM5560 - reasons for disconnection from Ethernet network

I have a client having the same issues with several 5560's. Those meters are all connected to Cisco Nexus switches and it seems to be an ARP issue on the network side. As soon as the meter is power cycles and re-broadcasts to the network they are immediately picked up and will operate for another 1-2 months without issue.

 

I have yet to find a solution other than power cycling the meters.

Share
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard
‎2020-04-21 10:47 AM
0 Likes
0
58
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-04-21 10:47 AM

Re: PM5560 - reasons for disconnection from Ethernet network

Hello @swil ,

 

1. What may be causing the problem explained?

Hard to say from just this explination. Could be that tcp connection at one end or the other is getting closes and not reset for example. Likely will need to contact technical support, ideally with some wireshark traces before and after the meter stops communicating. Given that meters downstream are able to talk I would say not a physical connection issue.

 

2. Is there a limit to the number of Schneider Ethernet meters that can exist on a Cat6a Ethernet string?

There is no hard limit that I am aware of. Something to consider is that at the first meter, all traffic to the string is seen and has to go through the same pipe. Which ethernet is fast, there will come a point where performance will degrade with more devices. I cannot say were that point is because many factors need to be included like type of device, how often you need to connunicate etc,

 

3. How can I stop this from happening?

Need to first determine what is happening to be able to stop.

 

4. If the IT department was to power cycle the switch periodically (eg. once a day or every few days), would this force all devices back online?

Depends on the device, I cannot speak for all the device types. The PM8000 meter has a setting TCP keep alive, If this is a non 0 number, if the meter sees no activity after this timeout the meter will close the connection. Now the caviate to this is if the software is able to detect the close, for example if the switch is down when the PM8000 sends the close packet, the software may no see this and think the connection is still open and still try to talk to the devices.

In the software, is it possible to close a connection to the device and try to open the connection again? If so, does this restore communication?

L4 Prime for Advanced metering and Utilities
Share
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard
‎2020-04-21 10:49 AM
0 Likes
0
57
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-04-21 10:49 AM

Re: PM5560 - reasons for disconnection from Ethernet network

Could this have to do with authentication on the switches? If an ARP is required to restore communication that may be indicate 802.1X with MAB is in use.

L4 Prime for Advanced metering and Utilities
Share
Reply
Ramasamy_N
Commander Ramasamy_N Commander
Commander
‎2020-04-28 09:56 AM
0 Likes
1
48
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-04-28 09:56 AM

Re: PM5560 - reasons for disconnection from Ethernet network

Hello @swil 

 

Can you please share the following data in mail to analyze this issue?

 

1.Communication network topology. Highlight the effected PM5560 in the diagram. 

2.What is firmware version of PM5560.

3.Copy and share the system.log file (from fw folder in FTP) from PM5560 meters.

 

Regards, 

Ramasamy N 

See Answer In Context

Share
Reply
swil
Lt. Commander swil
Lt. Commander
‎2020-05-12 06:47 PM
0 Likes
0
40
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-05-12 06:47 PM

Re: PM5560 - reasons for disconnection from Ethernet network

Thank you Ramasamy. Will get in touch if/when returning to site.

Share
Reply
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
142
Robert_Lee
Captain Robert_Lee Captain
56
Ramasamy_N
Commander Ramasamy_N Commander
40
DanL
Lt. Commander DanL Lt. Commander
31
Nedjma
Nedjma Community Alumni (Retired)
24
Daniel_Brandao
Lt. Commander Daniel_Brandao Lt. Commander
17
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.