PM5560 meter have a feature of two communication port (modbus and Ethernet) can we utilize both port and connected to PLC and RTU and pull the data in the same time
Link copied. Please paste this link to share this article on your social media post.
Hi Basim,
You can use the RS-485 port as well as the Ethernet port to pull data simultaneously from the meter.
Thank you,
Basem