I have a customer looking to upgrade some fairly ancient PM5560 meters, and there is a some confusion on the complete upgrade path. Based on the meter's User Manual (Firmware upgrades - PM5500 (schneider-electric.com), the FTP server is used for firmwares 2.0 and up. This document doesn't even mention DLF-3000:
However, FA237920 (Video: Firmware upgrade on a PM800, PM5XXX, PM200, PM700, CM4000/T, CM3000 and CM2000 series meters ...) states that DLF-3000 should be used up to version 1.01:
I understand the customer has several meters in the 1.X range, and I'd like to know whether they should use DLF-3000 or the FTP server for upgrades.
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Hello @RobGraham,
Please check this FAQ.
If the meter's FW is earlier than Firmware V1.01.00, then download V1.01.00 and see FA237920 for a walkthrough on upgrading using DLF-3000.
Once the meter is in FW 1.01.0 (or newer), you can upgrade to FW 2.3.0 using the FTP method.
Regards,
JD
Link copied. Please paste this link to share this article on your social media post.
Hello @RobGraham,
Please check this FAQ.
If the meter's FW is earlier than Firmware V1.01.00, then download V1.01.00 and see FA237920 for a walkthrough on upgrading using DLF-3000.
Once the meter is in FW 1.01.0 (or newer), you can upgrade to FW 2.3.0 using the FTP method.
Regards,
JD