Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Link copied. Please paste this link to share this article on your social media post.
Hello,
We use DO1 count of PM5320 to outpu of energy pulsing.
What value does the counter roll over by?
[DO1 count]
Digital Outputs Status
Base Unit - Digital Output DO1
Count (Modbus Register 9675 INT32U)
The register is INT32U, the maximum value of INT32U is 4,294,967,295 (=2^32-1).
Thus I think the roll over value is also 4,294,967,295 (=2^32-1).
Is my understanding correct?
Thank you.
Link copied. Please paste this link to share this article on your social media post.
Hello,
Yes, you are right.
The DO count and on time counters will be roll over after 4,294,967,295 counts.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Thank you very much for your kind answer.
It became very cleasr for me!
Thank you.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.