I'm struggling to work out how to enable the External mode for the digital output for the PM3255. Is this dependent on the firmware or possibly some other setting? I've been through the configuration on the meter itself and only get 3 options for both DO1 and DO2. Any ideas out there?
Link copied. Please paste this link to share this article on your social media post.
Hi Paul,
You can change the DO mode to External from the meter front panel. Go to Setup->DO->Mode.
However be aware that DO can be set to external mode only if you have fw 1.0.500 and greater.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Thanks, I had a feeling it was firmware related!! Cheers
Link copied. Please paste this link to share this article on your social media post.
Is it possible to upgrade the meter firmware for the PM3255?
Link copied. Please paste this link to share this article on your social media post.
As far as i know the answer is NO. Just confirm with tech support once.
Link copied. Please paste this link to share this article on your social media post.
Hi Paul,
PM3255 firmware field upgrade feature will be available, only for the meters which will be manufactured from March 2017.
Link copied. Please paste this link to share this article on your social media post.
I have a power meter pm3255 with firmware v01.05.0 , I have enabled external control for digital outputs. I am failing to write to the meter getting response 3000.